Greetings All,
Thank-you to all who have responded to my question on GR-1089. This group has
always shown its value.
Richard.
-----Original Message-----
From: Georgerian, Richard
Sent: Tuesday, November 18, 2003 9:34 AM
To: 'IEEE emc-pstc'
Subject: GR-1089 Issue 3: 3.2.1 Radiated Emission Criteria
Greetings All,
Hopefully someone has some insight to the following-
In GR-1089 Issue 3, Section 3.2.1, requirement R3-1 [8] uses the FCC
Class A
and B limits for equipment with no doors or covers for the range of 30MHz to
1GHz. It also has limits for below 30MHz and above 1GHz. This section I
understand. What I don't understand clearly is requirement R3-3 [10]. It
references emissions from Class A and B unit's not exceeding Table 3-2. Table
3-2 limits are higher than the FCC Class A and B limits. The doors or covers
are to be opened during emission testing. However, if the doors and covers
that are not intended to be opened during EUT operation, maintenance, and/or
repair need not be opened, I can still test to those higher limits. If so, I
can no longer can be considered FCC A or B equipment. Is requirement R3-3 [10]
mainly for central office areas and not residential?
Thanks.
Richard
=====
Richard Georgerian
Compliance Engineer
Carrier Access Corporation
5395 Pearl Parkway
Boulder, CO 80301
USA
Tele: 303-218-5748 Fax: 303-218-5503
mailto:[email protected]