Joe,
 
There should be no problem to find min. 400 V surge protectors - they are
readily available. I recently had this problem with a manufacturer of an
office appliance and they were able to find a similar surge protector rated
for the higher breakover voltage. 
 
If you need to locate a source for min. 400 V breakover surge protectors,
please let me know. 
 
I am sure that the fax, modems, PBXs out there which have been certified are
mounted with surge protectors with a breakover voltage of 1.6 Vrated of the
equipment. 
 
 
Best Regards,
 
Peter

Joe Randolph <[email protected]> wrote:


Hello All:

While we are on the subject of TNV-to-earth insulation, I would like to
pose a related question regarding clause 6.1.2.1 in EN 60950-1 and the
deviations in Annex ZB for Finland, Sweden, and Norway. This question
relates to the requirement that "surge suppressors that bridge the
insulation shall have a minimum breakover voltage of 1.6 times the rated
voltage.....". 

Suppose I have a piece of office equipment that is powered from the AC
mains and has a rated voltage of 250 VRMS. The equipment also has a
connection to a TNV-3 phone line. It uses a 3-wire AC mains plug that
includes an earth ground. 

Inside the equipment, the surge protection on the TNV-3 phone line
includes two 300 volt surge protectors, connected from tip to ground and
>from ring to ground (there is a third surge protector connected across
tip! and ring, but that is incidental to the question at hand). I have
seen this type of construction many times, and I believe it is widely
used in the industry.

Now, if I evaluate this construction for compliance with clause 6.1.2.1,
I quickly conclude that the two surge protectors connected tip-to-ground
and ring-to-ground must have a minimum breakover voltage of no less than
(1.6)x(250) = 400 volts. 

Okay, this looks like a problem, but the exclusions in clause 6.1.2.2
leave some wiggle room. This particular piece of office equipment is
not permanently connected, nor is it installed by a service person.
However, it is possible to equip it with provisions for a permanent
earthing conductor and then provide instructions for the installation of
that conductor. Never mind how many users will actually read the
instructions....

Now I go to Annex ZB and look at the deviations to clause 6.1.2.2 for
Finland, Norway, and Sweden. The exclusions described here are much
more restrictive, limited to permanently connected equipment or
pluggable equipment type B, used in restricted access locations where
equipotential bonding has been applied. In other words, a telephone
central office or *maybe* the main telephone closet in an office
building. Certainly, no stretch of the imagination would have this
clause include the typical office environment.

So, does this equipment fail to comply with EN 60950-1 for use in
Finland, Norway, and Sweden? It appears to me that it fails to comply,
but I can tell you there is a lot of product out there that meets this
description. Think modems, fax machines, and small PBXs.

I would like to hear what others in the group think. Am I missing
something here?


Thanks,

Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at: http://www.ieee-pses.org/

To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard: [email protected]
Dave Heald: [email protected]

For policy questions, send mail to:
Richard Nute: [email protected]
Jim Bacher: [email protected]

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


  _____  

Do you Yahoo!?
Yahoo! Hotjobs: Enter the "Signing Bonus" Sweepstakes
<http://pa.yahoo.com/*http://us.rd.yaho
.com/hotjobs/mail_footer_email/evt=2148
/*http://hotjobs.sweepstakes.yahoo.com/signingbonus> 

Reply via email to