http://www.ieee-pses.org/symposium http://www.emc2004.org/
-------------------------------------------------- 
Group,
 
UL recently changed the 943 standard, which applies to GFCI breakers.
Previously there was a test for conducted immunity which used a special test
fixture to inject a signal onto the line input, with the neutral conductor
grounded. This was essentially a differential mode test. The test was
performed at a 0.5v level, at frequencies up to 450MHz. It was performed only
on the input side, not the output side.
 
One of the (many) changes to the standard was to perform the conducted
immunity test using the 61000-4-6 test method (a common-mode test). But, they
kept the 0.5v level.  
 
The only reason I can think of that the 0.5v test level was kept was because
that was the level previously used.  It makes no sense to me why a breaker
should only meet a 0.5v test level, when anything that plugs into the circuit
being protected by the breaker must meet a 3v or 10v level. 
 
I am hoping to get some input here so that I can convince people we need to be
testing to a higher level.
 
Thanks in advance.
 
Bob Richards, NCT
Square D.
 
------------------------------------------- 

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. 


IEEE PSES Main Website: http://www.ieee-pses.org/ 


To post a message send your e-mail to [email protected] 


Instructions for use of the list server: 


http://listserv.ieee.org/listserv/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Ron Pickard: [email protected] Dave Heald: [email protected] 


For policy questions, send mail to: 


Richard Nute: [email protected] Jim Bacher: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc


Reply via email to