>We have a customer who has had their declaration of conformity
>questioned by the purchaser. The equipment is a 42U 19 inch rack, with
>approx 40 ITE products within it. the rack is fed from a single phase
>63A socket. The total load is approx 45A. the whole rack has been tested
>by a USA safety lab to EN60950 3rd edition. the (UK ) end customer is
>now questioning whether the DoC should reference BS7671 (UK's Wiring
>Regulations)

No. See below. As is not uncommon, the customer doesn't know its
posterior from its caudal flexure.

>with the result of the 63A feed being hardwired, secondary
>earthing being implemented to meet the earth-leakage requirement and the
>power distribution being redesigned to prevent "daisy-chaining"
>pluggable earth connections. Over the years we have EMC tested many
>racks but never seen one which did not have pluggable mains connectors.
>Each 'component' within the rack draws a max of 2A most at 0.5A We do
>not have safety expertise within the company, so I asking this question
>of the forum.
>
>"Is EN60950 the right standard for power distribution inside a rack?""

Yes. BS7671 is a national standard; it's not harmonised under the LVD
and it only has extremely limited application to load equipment. However
that 'limited application' means that you should check that the internal
wiring does not *conflict* with anything in BS 7671 and that the
earthing is *consistent* with Section 607 of BS 7671.
--
Regards, John Woodgate, OOO - Own Opinions Only.
The good news is that nothing is compulsory.
The bad news is that everything is prohibited.
http://www.jmwa.demon.co.uk Also see http://www.isce.org.uk


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to