Pierre,
 
For North America, you will need to consider the applicability of the
following, particularly the long (signal) cable that may go from inside to
outside plant:
 
1. (US) - National Electrical Code - NFPA 70 - Article 800 - Communications
Circuits
  a.  Flammability of cable - after 3 meters, you must meet the appropriate
flammability rating of the cable.  Your signal cable is considered a "wick"
for spreading flame, and may be part of a "multi-wick flame-spreading system"
if it is bundled.  There is a flammability hierarchy, starting with suffix X,
as in type CMX, for limited-use cable (does not apply to you), going to CM or
CMG  (general use, not going up verticle shaft to other floors), then CMR (for
"riser cable") then finally CMP (for "plenum cable" or cable suitable for use
in ducts, plenums, and other space used for environmental air handling.
b.  Primary Protector - If your cable is run from building to building, and
its length of 100 meters implies that it is a candidate for this, it will need
to be fitted with a Listed primary protector (essentially a voltage surge
protector) as close to practicable to the building entrance.
 
2.  (Canada) Canadian Electrical Code, Part I, CSA C22.1 - Section 60 -
Electrical Communications Systems
Everything that is mentioned above for the US goes for Canada, as well.  These
sections are not written in the same text, but the requirements are very much
harmonized.
 
3.  (US/Canada)  - UL 60950-1/CSA C22.2 No. 60950-1 -03 - 
 
a.  Clause 6.4 - Protection Against Overvoltage from Power Cross - 
Since your cable is running to outside plant, you have to consider whether it
is long enough that it may become exposed to power cross, or contact with
overhead AC mains supply conductors.  Your earthed shield on your cable will
not be sufficient to protect you against this phenomena.  There are
relaxations for campus environment runs.
 
b.  Listed Cable - for the US and  Canada, the cable you select will need to
be Listed(US)/Certified (Canada) for the types mentioned above.  They cannot
be only Recognized Appliance Wiring Material (AWM) for the lengths you are
considering.
 
As far as earthing your cable, yes, it should be done, but you will probably
find limited, if any, mandatory requirements on doing so.
 
Hope this helps,
 


Don Gies, N.C.E
Senior Product Compliance Engineer
Lucent Technologies - Bell Labs
Holmdel, NJ 07733 USA

 
 
 
 
 
 

From: [email protected] 
mailto:[email protected]]On Behalf Of Pierre Selva
Sent: Monday, March 14, 2005 8:40 AM
To: 'Forum Safety-emc'
Subject: Grounding, Earthing of long cables


Hello all,
 
The grounding/earthing of long distance cables (more than 100m) concern the
EMC and Safety matters.
I’m looking for some documentation / information on how to perform a good
connection to earth of this kind of cables. Mainly, I would like to know what
are the normative and regulatory documents which apply in the North America
and in Europe. 
My main interest is to identify the difference (if exist) between official
rules and use and to know exactly what I have to do on communication lines
(like RS485, LAN …) or other long lines when they go outside the building.
 
I know that in UK the BS7671 applies. What are the other applicable standard
in Europe and in the US/Canada ? 
Do you know where I can find interesting documentation on this subject ?
(except on this forum, of course !)
 
Many thanks in advance,
 
Best regards,
Pierre
 
 
Pierre SELVA
Product certification manager
EMITECH Rhône Alpes
1 rue des Essarts
38610 GIERES - France
Ph : +33 (0)4 38 370 007
Fx : +33 (0)4 38 371 004
GSM : +33(0)6  76 63 02 58
[email protected]
 <http://www.emitech.fr> www.emitech.fr
 
---------------------------------------------------------------- This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 
To post a message to the list, send your e-mail to [email protected] 

Instructions: http://listserv.ieee.org/listserv/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas [email protected] Mike Cantwell [email protected] 

For policy questions, send mail to: 

Richard Nute: [email protected] Jim Bacher: [email protected] 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 
---------------------------------------------------------------- This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 
To post a message to the list, send your e-mail to [email protected] 

Instructions: http://listserv.ieee.org/listserv/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas [email protected] Mike Cantwell [email protected] 

For policy questions, send mail to: 

Richard Nute: [email protected] Jim Bacher: [email protected] 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 


Reply via email to