Isn't the point of CDN blocking caps to be transparent at the rf or
transient spectrum and only block the power line frequency?  I think the
blocking cap impedance should be negligible relative to 150 Ohms over the
spectrum which makes up the EFT.

> From: Doug Smith <[email protected]>
> Organization: D. C. Smith Consultants
> Reply-To: [email protected]
> Date: Sat, 13 Aug 2005 09:19:18 -0700
> To: Ken Javor <[email protected]>
> Cc: EMC-PSTC - Forum <[email protected]>
> Subject: Re: Capacitive Clamp insertion loss
> 
> Hi Ken and the group,
> 
> The higher level for the power lines is because EFT only occurs on
> power lines and couples to I/O lines. The capacitive clamp is meant to
> simulate the coupling mechanism, but is, in my experience, nowhere
> near what really happens. The clamp also has an inductive component
> and combined with its dimensions is why is is (unintenionally)
> directive which in turn sends more energy in the wrong direction.
> 
> Still not sure what is meant by 6 dB insertion loss of the capacitive
> clamp. I would like to see how the lab thinks that is to be
> defined/measured.
> 
> The generator impedance is 50 Ohms and is fed into the clamp directly.
> The CDN couples the generator onto powerlines dirctly through
> capacitors so the source impedance is not 150 Ohms. The load of course
> is not anything like 150 Ohms most of the time for this broad band
> stress (bandwidth about a few hundred MHz).
> 
> Doug
> 
> Ken Javor wrote:
>> I haven't watched these tests performed, nor performed them, so I am not in
>> any way an expert.  But I see a flaw in the logic.  When any of the
>> requirements implemented with a CDN call out a test potential, it is cited
>> as an open circuit potential with a 150 Ohm source impedance.  Since good rf
>> measurement practice (at least at high frequencies) would be to calibrate
>> the CDN-injected potential into 150 Ohms, the matched potential would indeed
>> be precisely 6 dB down from the open-circuit limit.  This is borne out by
>> the fact that the AE side of the CDN is supposed to be an impedance much
>> higher than 150 Ohms, so it wouldn't load the shunt-injected signal.
>> 
>> So if the capacitive clamp truly has a 6 dB insertion loss, then it should
>> inject precisely the same value as the CDN, when both devices are fed with
>> the same potential, and loaded by 150 Ohms.
>> 
>> My guess (and it is just that) is that the rationale for a higher test level
>> on the ac lines vs. the signal lines is that the ac lines are generally
>> longer and are more efficient pickups.
>> 
>> 
>>> From: "Jim Eichner" <[email protected]>
>>> Date: Fri, 12 Aug 2005 11:38:29 -0700
>>> To: "EMC-PSTC - Forum" <[email protected]>
>>> Subject: Capacitive Clamp insertion loss
>>> 
>>> 
>>>> A lab we're using has an interpretation of EFT testing that never
>>>> occurred to me.  I'm interested in other people's understanding and
>>>> opinions.  Please feel free to point me to the archives if this has
>>>> been discussed before.
>>>> 
>>>> The generic immunity standard EN61000-6-1 calls out EFT on different
>>>> types of ports, and gives the applied test level.  For signal ports
>>>> it's a 500V test using the clamp and for AC ports it's 1000V using a
>>>> CDN.  If the clamp has a 6dB insertion loss, as our lab claims, then
>>>> the 500V spec in the standard results in application of 250V to the
>>>> EUT cable.  Presumably the authors of the standard know that and
>>>> accounted for it.   The CDN directly couples without 6dB of loss so
>>>> presumably the authors said 1000V with the intent of the EUT cable
>>>> actually seeing 1000V.
>>>> 
>>>> So what do you do for an AC port that draws more current than the CDN
>>>> available is rated for?
>>>> 
>>>> The lab's answer is to use the cap clamp, but because of the 6dB
>>>> insertion loss they doubled the generator setting to 2kV to obtain the
>>>> 1kV test that the standard calls for.  Opinions?  Comments?
>>>> 
>>>> In 61000-4-4 it says that if the line current is higher than the
>>>> specified current capability of the CDN you should use a 33nF coupling
>>>> cap per figure 10, in which case the EUT would be powered directly
>>>> from the grid and the EFT generator's connection to the EUT is via the
>>>> coupling cap and appropriate grounding provisions (another question is
>>>> what that looks like).  I may end up insisting that the lab use this
>>>> approach, but in the meantime I wanted to get the forum's opinion on
>>>> the cap. clamp method discussed above.
>>>> 
>>>> Thanks,
>>>> 
>>>> Jim Eichner, P.Eng.
>>>> Compliance Engineering Manager
>>>> Xantrex Technology Inc.
>>>> e-mail: [email protected]
>>>> web: www.xantrex.com
>>>> Any opinions expressed are those of my invisible friend.
>>>> Confidentiality Notice: This email message, including any attachments,
>>>> is for the sole use of the intended recipient(s) and may contain
>>>> confidential and privileged information. Any unauthorized review, use,
>>>> disclosure or distribution is prohibited. If you are not the intended
>>>> recipient, please contact the sender by reply e-mail and destroy all
>>>> copies of the original message.
>>>> 
>>> 
>>> ----------------------------------------------------------------
>>> This message is from the IEEE Product Safety Engineering Society
>>> emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
>>> 
>>> To post a message to the list, send your e-mail to [email protected]
>>> 
>>> Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html
>>> 
>>> List rules: http://www.ieee-pses.org/listrules.html
>>> 
>>> For help, send mail to the list administrators:
>>> 
>>> Scott Douglas             [email protected]
>>> Mike Cantwell            [email protected]
>>> 
>>> For policy questions, send mail to:
>>> 
>>> Richard Nute:           [email protected]
>>> Jim Bacher:             [email protected]
>>> 
>>> All emc-pstc postings are archived and searchable on the web at:
>>> 
>>> http://www.ieeecommunities.org/emc-pstc
>>> 
>> 
>> 
>> ----------------------------------------------------------------
>> This message is from the IEEE Product Safety Engineering Society
>> emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
>> 
>> To post a message to the list, send your e-mail to [email protected]
>> 
>> Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html
>> 
>> List rules: http://www.ieee-pses.org/listrules.html
>> 
>> For help, send mail to the list administrators:
>> 
>> Scott Douglas             [email protected]
>> Mike Cantwell            [email protected]
>> 
>> For policy questions, send mail to:
>> 
>> Richard Nute:           [email protected]
>> Jim Bacher:             [email protected]
>> 
>> All emc-pstc postings are archived and searchable on the web at:
>> 
>> http://www.ieeecommunities.org/emc-pstc
>> 
>> 
> 
> -- 
> -------------------------------------------------------
> ___          _       Doug Smith
> \          / )      P.O. Box 1457
> =========          Los Gatos, CA 95031-1457
> _ / \     / \ _       TEL/FAX: 408-356-4186/358-3799
> /  /\  \ ] /  /\  \     Mobile:  408-858-4528
> |  q-----( )  |  o  |    Email:   [email protected]
> \ _ /    ]    \ _ /     Website: http://www.dsmith.org
> -------------------------------------------------------
> 
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
> 
> To post a message to the list, send your e-mail to [email protected]
> 
> Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html
> 
> List rules: http://www.ieee-pses.org/listrules.html
> 
> For help, send mail to the list administrators:
> 
> Scott Douglas             [email protected]
> Mike Cantwell            [email protected]
> 
> For policy questions, send mail to:
> 
> Richard Nute:           [email protected]
> Jim Bacher:             [email protected]
> 
> All emc-pstc postings are archived and searchable on the web at:
> 
> http://www.ieeecommunities.org/emc-pstc
> 


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to