> A lab we're using has an interpretation of EFT testing that never
> occurred to me.  I'm interested in other people's understanding and
> opinions.  Please feel free to point me to the archives if this has
> been discussed before.
> 
> The generic immunity standard EN61000-6-1 calls out EFT on different
> types of ports, and gives the applied test level.  For signal ports
> it's a 500V test using the clamp and for AC ports it's 1000V using a
> CDN.  If the clamp has a 6dB insertion loss, as our lab claims, then
> the 500V spec in the standard results in application of 250V to the
> EUT cable.  Presumably the authors of the standard know that and
> accounted for it.   The CDN directly couples without 6dB of loss so
> presumably the authors said 1000V with the intent of the EUT cable
> actually seeing 1000V.
> 
> So what do you do for an AC port that draws more current than the CDN
> available is rated for?  
> 
> The lab's answer is to use the cap clamp, but because of the 6dB
> insertion loss they doubled the generator setting to 2kV to obtain the
> 1kV test that the standard calls for.  Opinions?  Comments?
> 
> In 61000-4-4 it says that if the line current is higher than the
> specified current capability of the CDN you should use a 33nF coupling
> cap per figure 10, in which case the EUT would be powered directly
> from the grid and the EFT generator's connection to the EUT is via the
> coupling cap and appropriate grounding provisions (another question is
> what that looks like).  I may end up insisting that the lab use this
> approach, but in the meantime I wanted to get the forum's opinion on
> the cap. clamp method discussed above.
> 
> Thanks,
> 
> Jim Eichner, P.Eng. 
> Compliance Engineering Manager
> Xantrex Technology Inc. 
> e-mail: [email protected] 
> web: www.xantrex.com 
> Any opinions expressed are those of my invisible friend.
> Confidentiality Notice: This email message, including any attachments,
> is for the sole use of the intended recipient(s) and may contain
> confidential and privileged information. Any unauthorized review, use,
> disclosure or distribution is prohibited. If you are not the intended
> recipient, please contact the sender by reply e-mail and destroy all
> copies of the original message.
> 


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to