Reginald,
Actually, I think you are outside of Class 2 limits
with 24 Vac 5 A, as the limits of Class 2 are maximum
30 Vac / 42.4 Vdc, maximum 8 A and maximum 100 VA.
Your power supply is over the 100 VA maximum.
That does also mean you are outside the UL 1310 limits
(Standards for Class 2 power units). I am not that
familiar with all the different UL requirements for
power supplies, but I did some digging around on
www.ul.com and found the following possibility:
Standard - UL 1012: Power Units Other than Class
2
Category - QQFU: [Power Supplies] Power Supplies,
General Purpose.
Hope that helps,
-Camille Good
Portland, Oregon
--- Reginald Henry <[email protected]> wrote:
> Info needed...
>
> I am trying to identify a UL Listed "Desktop or
> Plugin " Power Supply.
>
> The Parameters are...
>
> Input 120vAC
> Output 24vAC @ 5amp
>
> The power supply would be for out door application
> .. meaning it is driving
> units that are outdoors but the supply itself is in
> doors.
> I do realize that I am possibly in the realm of
> Class 2 NOT Wet Class 3 Wet
>
> However, with my output requirements would this mean
> that I would exceed the
> limits of UL 1310 and must look for a power supply
> other than one that will
> meet the Ul 1310 standard ? i.e., maybe use a
> transformer standard, ?
>
> Please advise
>
>
> Regards,
> Reg Henry
> Reginald Henry
>
>
>
>
> This e-mail message may contain privileged or
> confidential information. If
> you are not the intended recipient, you may not
> disclose, use, disseminate,
> distribute, copy or rely upon this message or
> attachment in any way. The
> company accepts no liability for any damage caused
> by any virus transmitted
> by this email. Furthermore, the company does not
> warrant a proper and
> complete transmission of this information, nor does
> it accept liability for
> any delays. If you received this e-mail message in
> error, please return by
> forwarding the message and its attachments to the
> sender.
>
>
>
> -
> 2005 IEEE Symposium on Product Safety Engineering
> 3-4 October Schaumburg, IL
> http://www.ieee-pses.org/symposium
>
>
> This message is from the IEEE Product Safety
> Engineering Society
> emc-pstc discussion list. Website:
> http://www.ieee-pses.org/
>
> To post a message to the list, send your e-mail to
> [email protected]
>
> Instructions:
>
http://listserv.ieee.org/listserv/request/user-guide.html
>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
>
> Scott Douglas [email protected]
> Mike Cantwell [email protected]
>
> For policy questions, send mail to:
>
> Richard Nute: [email protected]
> Jim Bacher: [email protected]
>
> All emc-pstc postings are archived and searchable on
> the web at:
>
> http://www.ieeecommunities.org/emc-pstc
>
-
2005 IEEE Symposium on Product Safety Engineering
3-4 October Schaumburg, IL
http://www.ieee-pses.org/symposium
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. Website: http://www.ieee-pses.org/
To post a message to the list, send your e-mail to [email protected]
Instructions: http://listserv.ieee.org/listserv/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas [email protected]
Mike Cantwell [email protected]
For policy questions, send mail to:
Richard Nute: [email protected]
Jim Bacher: [email protected]
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc