A couple comments.  A strip line test might be a substitute for an rf
conducted immunity test, if the stripline were long enough to illuminate the
entire cable harness, which is at least within the realm of the possible for
equipment slated for placement on a passenger bus.  The 15 cm stripline height
is commensurate with a CI requirement which stops at 80 MHz.  However the
audio frequency CI test mentioned below has nothing whatever to do with the
original rf CI requirement mentioned by Mr. Price.  The audio CI requirement
is a differential mode test meant to simulate power-quality-related 
electrical bus ripple potential, whereas the rf CI requirement is common mode
and reflects a concern with intentional rf transmissions coupling to cables
within the passenger bus.



From: "Chileshe, Chris" <[email protected]>
List-Post: [email protected]
Date: Tue, 21 Feb 2006 16:18:17 -0000
To: <[email protected]>
Subject: RE: EN61000-4-6:1996




Ed,

I'll state right the outset that this e-mail does not answer any of your
questions. I am only commenting
on the test request.

It really sounds to me like your customer wants to perform the automotive
equivalent to the conducted 
immunity test of EN 61000-4-6. The ideal candidate for the frequency range
(presumed 150kHz to 80MHz)
is the stripline test of ISO 11452-5. The severity test levels can be
correlated with free-field according to 
Annex B of this standard (correct for 150mm stripline)

I prefer the Bulk Current Injection (BCI) test method of ISO 11452-4 for
equipment in plastic enclosures for
reasons of the effects of fringe fields from stripline plates near the EUT.
Unfortunately, the ISO standard
specifies a 1MHz lower limit on the frequency range.

Applying the ISO 11452 group of immunity standards offers your customer
compliance with the radiated
immunity requirements of automotive directive 2004/104/EC.  

Another test that could apply is the audio-frequency coupled noise immunity
test of SAE J1113 SEP96 
Sec 2 specified for 30Hz to 50kHz. The worst severity level I have received in
a customer specification 
is 3V pk-pk for a piece of equipment specified for 100V/m immunity (
free-field).

I just wonder if this is a case of the wrong standards - albeit more
"familiar" ones - being applied to a 
product.

Rgds

- Chris

O.O.Only.




From: [email protected] [mailto:[email protected]]On Behalf Of Price, Ed
Sent: 21 February 2006 15:13
To: [email protected]
Subject: EN61000-4-6:1996

I have been asked to do a Conducted Immunity test per BS EN61000-4-6:1996 on a
gadget that mounts on the inside wall of a bus (and is accessible to the
passengers). First, I think this isn't the latest version of this
specification, but it is what the customer requested.

This device has a completely non-conductive outer case. The only conductive
point is on it's rear, where a 15-pin "D" connector supplies vehicle power
through a shielded, twisted-pair cable.

The customer asked for a "direct connection" test, as shown in Figure 2a, with
a test level of 20 Volts. It seems to me that I will need to be able to
generate about 100 Vpp and 200 Watts from my RF amplifier. Does the requested
test level seem a bit extreme for a passenger bus application?

Further, I don't understand how to measure the voltage Uo. Is this the voltage
across the output of my 50-ohm RF source, or the voltage from the test
specimen injection point to ground?

And finally, Figure 2a implies a conductive test specimen case. How do you do
this test for a non-conductive case, where the only conductive surface
available is the length of the shielded power cable?

I'd appreciate any comments or guidance.

Regards,

Ed Price
[email protected]                   WB6WSN
NARTE Certified EMC Engineer & Technician
Electromagnetic Compatibility Lab
Cubic Defense Applications
San Diego, CA USA
858-505-2780 (Voice)
858-505-1583 (Fax)
Military & Avionics EMC Is Our Specialty


- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas [email protected] Mike Cantwell [email protected] 

For policy questions, send mail to: 

Jim Bacher: [email protected] David Heald: [email protected] 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 


- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list.    Website:  http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 

Instructions:  http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas           [email protected] Mike Cantwell          
[email protected] 

For policy questions, send mail to: 

Jim Bacher:             [email protected] David Heald:           
[email protected] 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 



- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to