Piotr,
 
I believe these clauses apply to ac or dc mains and protective earth 
connections, you can connect signal lines any way you like.
 
Regards,
 
David Gelfand
Product Integrity
Mitec Telecom Inc
9000 Trans-Canada Highway
Pointe-Claire, QC
Canada H9R 5Z8
514 694 9000 x2262 

  _____  

From: [email protected] [mailto:[email protected]] On Behalf Of Piotr Galka
Sent: 31 août 2006 07:44
To: EMC-PSTC
Subject: EN 60950-1 and 3.5mm terminal blocks


All,
 
Can I use 3.5mm terminal blocks in device under EN 60950-1 ?
 
Device is powered by 12V DC LPS source.
For connecting external signals (5V OC 2mA) cables with 0.5mm diameter wires 
(0.2mm2) are used.
Each conductor is single wire so I understand these are not flexible cords.
 
3.5mm terminal blocks accept 0.14mm2 to 0.75mm2, but  EN 60950-1 3.3.4 needs 
for other cables (as not flexible cords than other) terminals accepting up to 
2.5mm2.
It looks that it is for all connections because:
3  Wiring, connections and supply
3.3 Wiring terminals for connection of external conductors
3.3.4 Conductor sizes to be connected.
 
I also worry if standard 3.5mm terminal blocks agree with EN 60950-1 3.3.6: 
"Terminals shall be so designed or located that the conductor cannot slip out 
when the clamping screws or nuts are tightened."
 
Do 5V 2mA signal lines really need so much care or I missed something.
 
Thanks in advance.
 
Piotr Gałka
- ---------------------------------------------------------------- This message 
is from the IEEE Product Safety Engineering Society emc-pstc discussion list. 
Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________


Reply via email to