Hi all,

At first I thought the discussion concerning simple current carrying 
capability.  Now I'm wondering if Brian was thinking about fusing current 
of traces (destruction point).  Maybe this will help:
http://www.ultracad.com/articles/fusing.pdf

Pat Lawler
SL Power Electronics Corp.

[email protected] wrote on 02/06/2007 05:56:16 AM:
> Just another two pee's worth of accumulated wisdom from way back in my
> Sewage days... (don't ask)

> We used 'ASTA certified' motor control centres, rated at 80kA fault
> currents, where the 2" x 1/4" copper bus bars were quite capable of 
tearing
> themselves away from their mountings on the occasion of a digger out on
> site going straight through a feed to a sludge pump.   Fault currents of
> that magnitude on all three lines of a bus bar system  exceeded the
> strength of the plastic bus bar holders.  (>800 Newtons rings a bell)

> Similarly, on a mains distribution PCB for use on small instrumentation
> pumping systems, we had two 1/4" tracks, one on either side of the PCB,
> Single phase, 240V, protected by a 32A Circuit Breaker.  The PCB was
> furnished with about ten or so IEC 240V 16 amp outlets.   The inevitable
> happened, a short circuit, line to neutral, and the long mains tracks 
tore
> themselves off the board before the trip operated, to leave them hot
> looking, but flapping around in space like skipping ropes.  I suspect 
there
> was significant heating of the track, i.e. adhesive softening, before 
this
> happened, but even so - not at all what we expected.  I suspected EM
> forces, but we simply went to hard wired after that, so never followed 
it
> up.
>
> The breakers were Motor start types, with a longer thermal response 
time,
> and DOL breaking capacity was 9kA.
>
> If a PCB track is used as an Earth, it must be expected to take a fault
> current of about 9kA until the fuse/breaker protection operates (mS).
> Happily, it'll only be a single conductor with no adjacent magnetic 
field
> to drive against - unless the mains conductor is very close by - like 
our
> Motor Distribution board example.   Once again, a mechanical problem! 
:-)

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to