If you go back to issue 2 for individual equipment the distances are 1500 mm
above the floor and 600 mm from the face of each equipment. For major systems
the height is the same but the horizontal measurements are are at the midpoint
of each on third sections within all within all equipment aisles and cross
aisles. That puts you at the center of the aisles from the meter to equipment. 

But this is issue 2 not 4 – and it’s sound pressure level not sound power
being measured there. I believe the ETSI equipvalent documents had sound power
measurements but I’ve forgotten the reference number

Gary

 

  _____  

From: [email protected] [mailto:[email protected]] On Behalf Of Finlayson
Joe-G3162C
Sent: Friday, April 13, 2007 6:20 AM
To: [email protected]
Subject: RE: NEBS GR 1089 Issue 4

 

Richard,

 

            The acoustic noise requirements are called in GR-63 Issue 3 as
opposed to GR-1089 Issue 4.  The test methods, as specified in GR-63 Issue 3,
are contained in ANSI S12.10 as well as other ANSI S12.12 and S12.54.  Have
you reviewed these documents for the information you are seeking?

 

Thx,

 

 

Joe

 

 

Joe Finlayson

Tel:   (508) 357-8273

Fax:  (508) 357-8289

Email:  <mailto:[email protected]> [email protected]

 

Motorola, Inc.

Embedded Communications Computing

46 Lizotte Drive

Marlborough, MA 01752

USA

  _____  

From: [email protected] [mailto:[email protected]] On Behalf Of Stone, Richard
Sent: Friday, April 13, 2007 9:04 AM
To: [email protected]
Subject: NEBS GR 1089 Issue 4

 

Group,

In reading this for Sound Power in DB for Acoustic Noise,

It doesn’t state the distance for the measurement device from the EUT in the
1089 document above, is it 1 meter?

Also it states different DB levels based on location with or without operator
present. Is there a consensus for location testing?

 

Thanks

Rich,

 

Richard Stone

Cantata Technology

75 Perseverance Way

Hyannis, MA 02601

Ph. 508 862 3311 Fax 508 862 3020

www.cantata.com

 


______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc -
---------------------------------------------------------------- This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 


To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc -
---------------------------------------------------------------- This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 


To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc


Reply via email to