Neven,

Might I suggest that you contact the USNC IEC / CISPR SC I TAG (e-mail
me separately and I can give you the contact information) about
joining)?  We can always use informed input on these standards.  The I
TAG just met last week, but we also carry on e-mail discussions.

The second opportunity, once you have established yourself on the TAG,
is to be appointed to the appropriate working groups in CISPR SC I.
These would be WG3 (for maintenance of CISPR 22) and WG2 (for the
development of CISPR 32).  Without strong reasons otherwise, CISPR 32
will be just like CISPR 22 in the area of conducted emissions testing on
telecommunications ports.

Ghery S. Pettit
Member, USNC IEC / CISPR SC I TAG
Co-convenor, CISPR SC I WG3



From: [email protected] [mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, May 10, 2007 10:40 AM
To: [email protected]
Subject: Re: ISN for Conducted Emission in accordance to CISPR 22 Ed
5.2:2006

Thanks to everyone who replied off- and online. I am trying to look into
the TECHNICAL aspects of these standards, and unfortunately my
conclusion is that they still haven't been thoroughly examined by anyone
who has much experience with the details and issues related to
differential high-speed multi-pair interfaces, such as balance,
conversion, and how to measure these parameters. I spent a number of
years in that area, and I am still not sure what measurement method is
better and more appropriate (it can depend on what you are trying to
see), and consequently what measured levels of balance and conversion
are "true" - as they depend on how they are measured. One thing that
appears evident is that a single-pair measurement is not appropriate as
e.g. 4-pair interface exhibits coupling between all 4 pairs (8 lines)
and relation between the common-mode and differential mode (i.e.
conversion) when only one pair is driven is not the same as when the
whole cable is driven by the !
 common 
mode (or all 4 pairs are driven by differential mode). The lack of the
appropriate measurement method for balance is the major reason why the
levels of LCL for SLCE ISN and the required balance for CDN cannot be
properly (realistically) defined, which in turn allows manufacturers of
these devices to build couplers with various characteristics that can
easily cause apparent failures.

That's one of the reasons why I find the currently available standards
inappropriate. I do not question the intent of the standards, as I
believe it is good, but as Ken Hall pointed out it appears there is
positive voting going on, without fully understanding the technical (and
economic) implications. The methods in the standards are plausible,
i.e., they seem to make sense to someone with general technical
background in EMC, but at the detailed level of the specific
application, e.g. Ethernet, they do not take into account the related
issues, which make some methods (IMO) completely unsuitable. That's why
I currently strongly prefer clamp-methods - they don't affect the cable
characteristics.

I know many have observed considerable differences in results (SLCE and
Immunity) depending on the test method, as e.g. in the mentioned paper
as well as in numerous conversations I had with test-engineers as well
as in my first-hand observations, but I wish to draw attention of the
EMC community to things that I see as the root-cause of these effects
and that I believe very few people actually looked at the same level.
Before they are thoroughly understood I don't think we are ready for the
standards in question in their current form and for CDN/ISN devices
currently on the market.

I do not sit on these standards and I am in no way associated with the
committees. All my observations are coming from reading the standards
and papers, my personal experience with issues observed on many projects
across many companies worldwide, and from my lab work trying to measure
and understand these issues, especially conversion mechanisms and
balance in the Ethernet and other high-speed differential-signaling
world.

Regards, Neven



 -------------- Original message ----------------------
From: "Grace Lin" <[email protected]>
> Hello Ken,
> 
> Thank you for pointing out the paper.  Sorry, I missed your
presentation.  I
> remember my friends discussed the topic after attending your
presentation.
> I believe the concern they had were measuement instrument and
necessity.
> 
> I have a difficulty to understand the technical implications of telcom
port
> requirement.  I am not challenging the CISPR committee.  I just need
some
> help to understand the requirement/necessity.  Telcom port measurement
is
> through the conducted method.  A telecom port does not directly
connect to
> (interfere) public utility/power network.  If it radiates, it should
be
> covered by the radiated emission measurement.
> 
> From a manufacturer point of view, telecom port measurement is not a
big
> deal if products pass.  Labs don't add additional fee for this test.
For
> in-house testing, there is not much work to setup a test site (using
the
> conducted emission site plus an ISN and adaptors).
> 
> Best regards,
> Grace
> 
> On 5/10/07, Hall, Ken <[email protected]> wrote:
> >
> >  Hello Grace,
> >
> > This topic has been argued and discussed, multiple papers, in
CISPR/I AND
> > CISPR/G since the early 80's. The problem may be/is political.
However, with
> > a few countries voting against the LCL requirements they ended up in
the
> > standard because > 75% of the voting countries approved.
> >
> > We need to influence  every countries voting membership to only vote
> > positive if they understand the technical implications of a
standard.
> > Attached is a paper from IEEE EMC 2001.
> >
> > Regards,
> >
> > KEn
> >
> >  ------------------------------
> > *From:* [email protected] [mailto:[email protected]] *On Behalf Of
*Grace
> > Lin
> > *Sent:* Thursday, May 10, 2007 4:00 AM
> > *To:* [email protected]
> > *Subject:* Re: ISN for Conducted Emission in accordance to CISPR 22
Ed 5.2
> > :2006
> >
> >
> >  Hi Neven,
> >
> > Thank you for the detail comments.  I suggest you write a paper to
the
> > IEEE International Symposium on EMC.  There are many EMC experts
attending
> > this Symposium, including many equipment manufacturers, rule makers,
and
> > government agencies.  The Symposium record is distributed worldwide
and kept
> > forever.  This is a good way to get attention and make friends.
> >
> > Grace
> >
> >
> > On 5/9/07, [email protected] <[email protected]> wrote:
> > >
> > > Be careful if you want to use ISN for Cinducted Emission or
Immunity
> > > testing of Ethernet or any other high speed differential-pair
interface. I
> > > just could not resist to reply, because of so poor specifications
which
> > > allow the ISN to cause APPARENT failures, and can cost the
industry millions
> > > to "fix" problems that do not exist. I tried to talk with a major
vendor of
> > > these devices, offering help to make them actually appropriate for
use with
> > > high-speed diff-pair interfaces ( e.g. Ethernet), but there
appears to
> > > be absolutely no interest. It appears there is too much politics
and
> > > marketing, as opposed to engineering, that dictates how these
devices are
> > > constructed (and specified). The cost is paid by the industry who
is then
> > > forced to follow the standards. I have worked on many cases where
after a
> > > reported emission failure, measured using ISN, the clamp-method (
e.g.
> > > VOltage and Current Clamp method) resulted in very different and
passing
> > > result.
> > >
> > > So here are some of my thoughts on this topic.They are mostly
based on
> > > the use of CDN/ISN for Immunity, but they really equally apply to
both SLCE
> > > and Immunity.
> > >
> > > *       The most recent 6100-4-6 standard specifies the
common-mode (CM)
> > > impedance Zcm (Table 3) at the EUT-port of the coupling device
> > > *       It also specifies that the Common-to-Differential mode
> > > conversion (defined by Longitudinal Conversion Loss or LCL) of the
CDN
> > > should be better than the conversion of a cable or the equipment
connected
> > > to the cable, whichever conversion is lower, i.e. whichever LCL
value is
> > > larger (Note in 6.2.1.2)
> > > *       The standard recognizes that a given method and coupling
device
> > > may not be appropriate for all types of devices under test, so it
allows for
> > > alternate test methods. Specifically, in 6.2 it says:
> > >
> > > "If CDNs are not suitable or available, other injection methods
can be
> > > used".
> > >
> > > *       The note in 6.2.1.2, regarding common to differential mode
> > > conversion, recognizes that the CDNs for multi-pair balanced lines
(e.g.
> > > UTP) may not be suitable:
> > >
> > > "Often, clamp injection needs to be applied to multi-pair balanced
> > > cables,
> > > because suitable CDNs might not be available." *
> > >
> > > *What defines "suitable" can be the major limiting factor
> > >
> > >
> > > *       Rules for selecting appropriate method are given in 7.1.
The
> > > main deciding factor for selection of the method is (again): "are
the CDNs
> > > suitable?", which could result in a subjective decision
> > > *       Conversion can be a problem with the currently available
CDN and
> > > can make it not-suitable for Ethernet lines
> > > *       Relatively well designed RJ45/Ethernet devices  can have
between
> > >        -40 dB and -46 dB conversion (2%-1% impedance balance)
> > > *       Ethernet devices, as well as other high-speed devices that
> > > utilize balanced differential pairs, are very sensitive to CM-DM
conversion
> > > *       It is critical that the conversion characteristics of any
> > > coupling devices be at least the same if not better than the
conversion by
> > > the well-designed signal lines used for the application
> > > *       In practice, on multi-pair balanced cables where all wires
are
> > > coupled (e.g. 8 wires of a CAT5 UTP), it is not easy to:
> > > -       specify how to measure conversion
> > > -       measure conversion
> > > -       specify required levels of conversion
> > > *       Lack of clear and appropriate method for measuring
conversion
> > > can also be a problem with currently pending draft CISPR22
emission
> > > standard.
> > > *       The problem lies in the fact that the CDN/ISN is inserted
into
> > > an otherwise well-balanced line. The design of the CDN/ISN is not
balanced
> > > (the standards lack realistic requirement and appropriate
verification
> > > method) and it creates mode-conversion, which can create apparent
CM
> > > emission and susceptibility. This condition does not resemble the
realistic
> > > situation were the cable is fairly balanced and uninterrupted
> > > *       Conversion by the CDN/ISN can be well beyond the
conversion
> > > characteristics of the cable. The currently specified test method
for
> > > measuring conversion (or LCL) is not appropriate for multi-pair
interfaces.
> > > *       Test equipment should not increase the conversion by
introducing
> > > imbalance considerably higher than that of the cable. Conversion
by the test
> > > equipment artificially increases the test levels beyond the
characteristics
> > > of the measured device and intended cabling, causing apparent
failures
> > >
> > >
> > > *       Therefore, unless better CDN/ISN devices are constructed
(and/or
> > > better-defined in the standards), I recommend methods using clamps
(e.g.
> > > Voltage and Current Clamp method), which preserve integrity of the
used
> > > cabling and allow testing in more realistic environment. The
CM-impedance
> > > requirement that can be of some concern with the clamp-methods is
not hard
> > > to meet, at least for 4-pair differential interfaces, but that is
another
> > > topic.
> > >
> > > I hope it helps make your decision.
> > >
> > >
> > >
> > > Regards, Neven
> > >
> > >
> > >
> > >
> > >
> > >
> > >  -------------- Original message ----------------------
> > > From: < [email protected]>
> > > > Hi,
> > > > this may be easier than you think (or wish).
> > > > To my knowledge there are only two manufacturers at the moment:
Teseq
> > > > and Fischer.
> > > >
> > > > Regards,
> > > > Ari Honkala
> > > >
> > > >
> > > >       On 5/8/07, wendy <[email protected] > wrote:
> > > >
> > > >               Dear All,
> > > >
> > > >
> > > >
> > > >               My company intends to purchase the above
mentioned. Will
> > > > someone recommend any brand/model that compiles to the latest
> > > > requirements?
> > > >
> > > >
> > > >
> > > >               Regards,
> > > >
> > > >               Wendy Nya
> > > >
> > > >               -
> > > > ----------------------------------------------------------------
This
> > > > message is from the IEEE Product Safety Engineering Society
emc-pstc
> > > > discussion list. Website: http://www.ieee-pses.org/
> > > >
> > > >               To post a message to the list, send your e-mail to
> > > > [email protected]
> > > >
> > > >               Instructions:
> > > > http://listserv.ieee.org/request/user-guide.html
> > > >
> > > >               List rules:
http://www.ieee-pses.org/listrules.html
> > > >
> > > >               For help, send mail to the list administrators:
> > > >
> > > >               Scott Douglas [email protected] Mike Cantwell
> > > > [email protected]
> > > >
> > > >               For policy questions, send mail to:
> > > >
> > > >               Jim Bacher: [email protected] David Heald:
> > > > [email protected]
> > > >
> > > >               All emc-pstc postings are archived and searchable
on the
> > >
> > > > web at:
> > > >
> > > >               http://www.ieeecommunities.org/emc-pstc
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >       -
> > > > ----------------------------------------------------------------
This
> > > > message is from the IEEE Product Safety Engineering Society
emc-pstc
> > > > discussion list. Website: http://www.ieee-pses.org/
> > > >
> > > >       To post a message to the list, send your e-mail to
> > > > [email protected]
> > > >
> > > >       Instructions:
http://listserv.ieee.org/request/user-guide.html
> > > >
> > > >       List rules: http://www.ieee-pses.org/listrules.html
> > > >
> > > >       For help, send mail to the list administrators:
> > > >
> > > >       Scott Douglas [email protected] Mike Cantwell
[email protected]
> > > >
> > > >
> > > >       For policy questions, send mail to:
> > > >
> > > >       Jim Bacher: [email protected] David Heald:
> > > > [email protected]
> > > >
> > > >       All emc-pstc postings are archived and searchable on the
web at:
> > >
> > > >
> > > >
> > > >       http://www.ieeecommunities.org/emc-pstc
> > > >
> > > >
> > > > -
> > > > ----------------------------------------------------------------
> > >
> > > > This message is from the IEEE Product Safety Engineering Society
> > > > emc-pstc discussion list.    Website:
http://www.ieee-pses.org/
> > > >
> > > > To post a message to the list, send your e-mail to
[email protected]
> > > >
> > > > Instructions:   http://listserv.ieee.org/request/user-guide.html
> > > >
> > > > List rules: http://www.ieee-pses.org/listrules.html
> > > >
> > > > For help, send mail to the list administrators:
> > > >
> > > >      Scott Douglas           [email protected]
> > > >      Mike Cantwell           [email protected]
> > > >
> > > > For policy questions, send mail to:
> > > >
> > > >      Jim Bacher:             [email protected]
> > > >      David Heald:             [email protected]
> > > >
> > > > All emc-pstc postings are archived and searchable on the web at:
> > > >
> > > >     http://www.ieeecommunities.org/emc-pstc
> > > >
> > >
> > >
> > >
> > > -
> > > ----------------------------------------------------------------
> > > This message is from the IEEE Product Safety Engineering Society
> > > emc-pstc discussion list.    Website:   http://www.ieee-pses.org/
> > >
> > > To post a message to the list, send your e-mail to
[email protected]
> > >
> > > Instructions:  http://listserv.ieee.org/request/user-guide.html
> > >
> > > List rules: http://www.ieee-pses.org/listrules.html
> > >
> > > For help, send mail to the list administrators:
> > >
> > >     Scott Douglas           [email protected]
> > >     Mike Cantwell           [email protected]
> > >
> > > For policy questions, send mail to:
> > >
> > >     Jim Bacher:             [email protected]
> > >     David Heald:             [email protected]
> > >
> > > All emc-pstc postings are archived and searchable on the web at:
> > >
> > >     http://www.ieeecommunities.org/emc-pstc
> > >
> > >
> > > ---------- Forwarded message ----------
> > > From: <[email protected]>
> > > To: < [email protected]>
> > > Date: Tue, 8 May 2007 11:17:17 +0000
> > > Subject: RE: ISN for Conducted Emission in accordance to CISPR 22
Ed 5.2
> > > :2006
> > >  Hi,
> > > this may be easier than you think (or wish).
> > > To my knowledge there are only two manufacturers at the moment:
Teseq
> > > and Fischer.
> > >
> > > Regards,
> > > Ari Honkala
> > >
> > >
> > >
> > > On 5/8/07, wendy <[email protected] > wrote:
> > > >
> > > >  Dear All,
> > > >
> > > >
> > > >
> > > > My company intends to purchase the above mentioned. Will someone
> > > > recommend any brand/model that compiles to the latest
requirements?
> > > >
> > > >
> > > >
> > > > Regards,
> > > >
> > > > Wendy Nya
> > > > -

> > > > This message is from the IEEE Product Safety Engineering Society
emc-pstc
> > > > discussion list. Website: http://www.ieee-pses.org/
> > > >
> > > > To post a message to the list, send your e-mail to
[email protected]
> > > >
> > > > Instructions: http://listserv.ieee.org/request/user-guide.html
> > > >
> > > > List rules: http://www.ieee-pses.org/listrules.html
> > > >
> > > > For help, send mail to the list administrators:
> > > >
> > > > Scott Douglas [email protected] Mike Cantwell [email protected]
> > > >
> > > > For policy questions, send mail to:
> > > >
> > > > Jim Bacher: [email protected] David Heald:
[email protected]
> > > >
> > > > All emc-pstc postings are archived and searchable on the web at:
> > > >
> > > > http://www.ieeecommunities.org/emc-pstc
> > > >
> > > >
> > > - ----------------------------------------------------------------
This
> > > message is from the IEEE Product Safety Engineering Society
emc-pstc
> > > discussion list. Website: http://www.ieee-pses.org/
> > >
> > > To post a message to the list, send your e-mail to
[email protected]
> > >
> > > Instructions: http://listserv.ieee.org/request/user-guide.html
> > >
> > > List rules: http://www.ieee-pses.org/listrules.html
> > >
> > > For help, send mail to the list administrators:
> > >
> > > Scott Douglas [email protected] Mike Cantwell [email protected]
> > >
> > > For policy questions, send mail to:
> > >
> > > Jim Bacher: [email protected] David Heald: [email protected]
> > >
> > > All emc-pstc postings are archived and searchable on the web at:
> > >
> > > http://www.ieeecommunities.org/emc-pstc
> > >
> > >            -
> > > ----------------------------------------------------------------
This
> > > message is from the IEEE Product Safety Engineering Society
emc-pstc
> > > discussion list. Website: http://www.ieee-pses.org/
> > >
> > > To post a message to the list, send your e-mail to
[email protected]
> > >
> > > Instructions: http://listserv.ieee.org/request/user-guide.html
> > >
> > > List rules: http://www.ieee-pses.org/listrules.html
> > >
> > > For help, send mail to the list administrators:
> > >
> > > Scott Douglas [email protected] Mike Cantwell [email protected]
> > >
> > > For policy questions, send mail to:
> > >
> > > Jim Bacher: [email protected] David Heald: [email protected]
> > >
> > > All emc-pstc postings are archived and searchable on the web at:
> > >
> > > http://www.ieeecommunities.org/emc-pstc -
> > > ----------------------------------------------------------------
This
> > > message is from the IEEE Product Safety Engineering Society
emc-pstc
> > > discussion list. Website: http://www.ieee-pses.org/
> > >
> > > To post a message to the list, send your e-mail to
[email protected]
> > >
> > > Instructions: http://listserv.ieee.org/request/user-guide.html
> > >
> > > List rules: http://www.ieee-pses.org/listrules.html
> > >
> > > For help, send mail to the list administrators:
> > >
> > > Scott Douglas [email protected] Mike Cantwell [email protected]
> > >
> > > For policy questions, send mail to:
> > >
> > > Jim Bacher: [email protected] David Heald: [email protected]
> > >
> > > All emc-pstc postings are archived and searchable on the web at:
> > >
> > > http://www.ieeecommunities.org/emc-pstc
> > >
> > >
> > >
> > - ----------------------------------------------------------------
This
> > message is from the IEEE Product Safety Engineering Society emc-pstc
> > discussion list. Website: http://www.ieee-pses.org/
> >
> > To post a message to the list, send your e-mail to [email protected]
> >
> > Instructions: http://listserv.ieee.org/request/user-guide.html
> >
> > List rules: http://www.ieee-pses.org/listrules.html
> >
> > For help, send mail to the list administrators:
> >
> > Scott Douglas [email protected] Mike Cantwell [email protected]
> >
> > For policy questions, send mail to:
> >
> > Jim Bacher: [email protected] David Heald: [email protected]
> >
> > All emc-pstc postings are archived and searchable on the web at:
> >
> > http://www.ieeecommunities.org/emc-pstc
> >
> >
> >
> 
> -
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
> 
> To post a message to the list, send your e-mail to [email protected]
> 
> Instructions:  http://listserv.ieee.org/request/user-guide.html
> 
> List rules: http://www.ieee-pses.org/listrules.html
> 
> For help, send mail to the list administrators:
> 
>      Scott Douglas           [email protected]
>      Mike Cantwell           [email protected]
> 
> For policy questions, send mail to:
> 
>      Jim Bacher:             [email protected]
>      David Heald:            [email protected]
> 
> All emc-pstc postings are archived and searchable on the web at:
> 
>     http://www.ieeecommunities.org/emc-pstc
> 



-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to