In message 
<[email protected]>, dated 
Tue, 19 Jun 2007, "Kunde, Brian" <[email protected]> writes:

>We would like to come up with an internal test to ball-park measure 
>electromagnetic fields at line frequency (50/60Hz) to satisfy our 
>customers when such requests are made regarding compliance to the EU's 
>Physical Agents Directive (2004/40/EC). Any advice regarding test setup 
>and test equipment would be appreciated.
> 
[snip]
> 
>1. For IT and Laboratory equipment, what EMF test method standard 
>should we be looking at? Is there a harmonized test standard?

For me, the problem is that there are too many standards that appear to 
include the power frequency range, without a clear indication of what 
applies and how. There is a Generic EN, which has not been offered by 
the CENELEC BT to the Commission for 'notifying' in the Official Journal 
because the Basic standard on which it depends for methods of 
measurement is not yet approved.

It has been stated that ITE is known not to present an EMF hazard and 
need not be tested, but I know of no such official statement, even 
though IMHO it's true. Lab equipment covers a huge range, some products 
being designed to produce quite strong magnetic fields outside the box, 
so you would need to consider each product on its merits.
> 
>2. What test equipment is required?  A Google search popped up a lot 
>of hand held products that claim to measure EMF. Would such products do 
>what we need?

It's very difficult to distinguish between the truly scientific ones and 
those offered to people who think they are 'electrosensitive'. The 
latter are often much too sensitive in terms of the ICNIRP exposure 
recommendations, so that the buyer actually gets a response even in very 
weak fields.

In principle, you need an r.m.s. meter with a three-axis sensor and one 
that is calibrated in amps per metre, since that is how the ICNIRP 
values are given. The ICNIRP 'reference value' is about 8 A/m at power 
frequency. If the field strength is higher, you have to analyse the 
distribution in space to see if the Basic Restriction is met. This is a 
fair bit more difficult but can be done.

Recent scientific papers have suggested that the ICNIRP values are lower 
than is justified, and indeed the IEEE values are higher. ICNIRP applied 
the 'precautionary principle' and it has been suggested that a 'safety 
factor' of around 50 was involved! This may be an exaggeration. But I 
have exposed my hands to 1000 A/m with no perceptible effect.
> 
>3. Is this approach doable, or have I embarrassed myself by even 
>proposing such a test?

Yes, it's doable, if insight is applied.

References

Guidelines for limiting exposure to time-varying electric, magnetic, and 
electromagnetic fields (up to 300 GHz), International Commission on 
Non-Ionizing Radiation Protection (ICNIRP)

BS EN 50392:2004 Generic standard to demonstrate the compliance of 
electronic and electrical apparatus with the basic restrictions related 
to human exposure to electromagnetic fields (0 Hz – 300GHz)

IEC 62311 Ed.1: Assessment of electronic and electrical equipment 
related to human exposure restrictions for electromagnetic fields (0 Hz 
- 300 GHz)

PD CLC/TR 50442:2005 Guidelines for product committees on the 
preparation of standards related to human exposure from [sic] 
electromagnetic fields
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
There are benefits from being irrational - just ask the square root of 2.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to