Over the last few years, our lab has seen GFCIs falsely trip during the
radiated immunity test at 3V/m (don't recall frequency) and by conducted
emissions caused by a motor speed controller (frequency drive).  In the
later case, fingers got pointed in all directions. If the GFCI trips for
any reason other than high leakage or line imbalance then is it the
fault of the GFCI?  Are there GFCIs on the market that specifically
designed for applications such as frequency drives where they are less
susceptible to conducted emissions and line harmonics?

We know the NEC requires GFCIs to be used in bathrooms, basements,
garages and on curtain products such as hair dryers, hot tubs and window
air conditioners, but in the workplace, where are GFCIs absolutely
required? 

Case in point, I know of a product which has a motorized spinning
platform with sandpaper with water running on it (wet sanding). The
frequency drive that runs the motor causes a GFCI to trip yet the
product passes conducted emissions (class A) and leakage current test
(about 1ma).  Is the problem with the product or the GFCI? Does a GFCI
have to be used with such a product? If so, are there alternate
solutions to using a GFCI such as providing addition earth ground
connections?

Thanks.

The Other Brian


From: [email protected] [mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, July 19, 2007 8:41 AM
To: [email protected]
Subject: RE: Cell/mobile phones destroying electronic devices

I have been doing some research over the past few months regarding the
susceptibility of GFCIs and AFCIs to interference.  I have yet to
uncover any documented evidence of cellular telephones or other wireless
devices interfering with these devices.  Even with the large antennas of
the wiring, it is difficult to couple enough energy to cause a problem.
GFCIs and AFCIs are somewhat susceptible to conducted interference, but
the designs have been greatly improved over the years.

As a general rule, you don't want GFCIs and AFCIs in circuits for life
safety applications.  They should not be used for fire alarm systems,
fire pump systems or emergency lighting.  These devices should
definitely be avoided for any application where a power interruption
will cause significant financial harm or put lives at risk.

As Doug Smith noted, Information Technology Equipment (ITE) should not
be used on GFCI circuits.  IEC 60950-1 allows an ITE device with a
non-locking plug to have an earth leakage current of up to 3.5 mA.  A
GFCI in North America is set to trip at around 5 mA.  If you plug in
your computer, monitor, printer, scanner, cell phone charger and
cordless phone base into a power strip on a GFCI protected circuit, you
may easily find it tripping regularly.

AFCIs work differently, but they too can be very susceptible to
conducted noise from ITE.  I have worked with some that are well tested
for immunity to conducted noise and some which regularly trip in ITE
environments.  In the interest of full disclosure, I will note that APC
is a subsidiary of Schneider Electric which also owns Square-D.  I am
aware of extensive testing of the Square-D devices for conducted
immunity and they are not among the devices for which I have found
problems.

Ted Eckert
American Power Conversion/MGE
http://www.apc.com/

The items contained in this e-mail reflect the personal opinions of the
writer and are only provided for the assistance of the reader. The
writer is not speaking in an official capacity for APC-MGE or Schneider
Electric.
The speaker does not represent APC-MGE's or Schneider Electric's
official position on any matter.


 

             "Tarver, Peter"

             <peter.tarver@san

             mina-sci.com>
To 
             Sent by:                  <[email protected]>

             [email protected]
cc 
 

 
Subject 
             07/18/2007 05:06          RE: Cell/mobile phones destroying

             PM                        electronic devices

 

 

 

 

 

 





All -

In a similar vein to this thread, in January of this year, I posted a
request for information regarding wireless phones interfering with GFCI
devices.  This same request was also posted on the EMC-PSTC and
Electrical Safety IEEE Community pages, in order to broaden the audience
and to alleviate one expressed concern regarding the confidentiality
statement that (no doubt) appears at the bottom of this e-mail.

Unfortunately, there's been no responses that I'm aware of.  I've
duplicated that request, below.  Any input would be appreciate.  If
there is a concern about passing the information through me, I can put
anyone interested in responding in touch with the appropriate staff at
the TIA.



***ORIGINAL REQUEST***

The TIA (Telecommunication Industry Association) is looking for any
information on incidents of wireless phones (cordless, cell, etc.)
interfering with ground fault circuit interrupters (GFCIs). If anyone
has any information relating to this, please let me know and I will
forward information to the interested group.


Regards,

Peter L. Tarver, PE
[email protected]

CONFIDENTIALITY
This e-mail message and any attachments thereto, is intended only for
use by the addressee(s) named herein and may contain legally privileged
and/or confidential information. If you are not the intended recipient
of this e-mail message, you are hereby notified that any dissemination,
distribution or copying of this e-mail message, and any attachments
thereto, is strictly prohibited.  If you have received this e-mail
message in error, please immediately notify the sender and permanently
delete the original and any copies of this email and any prints thereof.
ABSENT AN EXPRESS STATEMENT TO THE CONTRARY HEREINABOVE, THIS E-MAIL IS
NOT INTENDED AS A SUBSTITUTE FOR A WRITING.  Notwithstanding the Uniform
Electronic Transactions Act or the applicability of any other law of
similar substance and effect, absent an express statement to the
contrary hereinabove, this e-mail message its contents, and any
attachments hereto are not intended to represent an offer or acceptance
to enter into a contract and are not otherwise intended to bind the
sender, Sanmina-SCI Corporation (or any of its subsidiaries), or any
other person or entity.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

LECO Corporation Notice:  This communication may contain confidential
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error.  Thank  you.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

Reply via email to