Heaven forbid we ever go back to the early 80’s when there was no acceptable 
methods, no accepted procedures, no accepted setup and when the FCC expected 
cable manipulation till the cows came home to find the maximum emissions 
levels.  Talk about a waste of time – days upon days moving every cable into 
every likely position finding the ‘worse’ case.  Then to find out that the FCC 
or another lab found that one cable position that showed 10dB more than the 
other lab measured.   Everyone was right in their own eyes and most of those 
eyes were blind except to their own erroneous methods and practices.

No, conformity of setup, table size, configuration, support equipment etc, may 
not be the best, but it is infinitely better than 30, even 25 years ago.

 

Dennis Ward 



Director of Engineering

American Certification Body 
Certification Resource for the Wireless Industry http://www.acbcert.com
703-847-4700 fax 703-847-6888 
direct - 703-880-4841

 

From: [email protected] [mailto:[email protected]] On Behalf Of Ken Javor
Sent: Tuesday, October 11, 2011 11:29 AM
To: 'EMC-PSTC'
Subject: Re: Table Size in Emissions test

 

Within his frame of reference, Ward is correct, which is why this entire 
accreditation process is flawed and broken.  We got along without it before, 
and it is adding nothing but extra costs and bureaucracy, and negative value to 
the process of controlling EMI.
 
Ken Javor

Phone: (256) 650-5261



________________________________

From: Dennis Ward <[email protected]>
Reply-To: <[email protected]>
List-Post: [email protected]
Date: Tue, 11 Oct 2011 11:15:00 -0700
To: 'Derek Walton' <[email protected]>
Cc: 'Grace Lin' <[email protected]>, 'WNya' <[email protected]>, 'EMC-PSTC' 
<[email protected]>
Subject: RE: Table Size in Emissions test

HI Derek
The point of anything ‘nominal’ is that it starts with what is expected and 
allows reasonable variations of sorts. And you hit the right words “relating to 
a designated or theoretical size”.  If you say you must follow the standard, 
then follow it. The designated size of a table is 1m x 1.5m x 0.8m.  This then 
is the size generally expected.  It is not a micrometer reading with 0.01m 
measurement uncertainty tolerances; it is a general designated and expected 
size – a nominal size.  
 
Now, and without going into uncertainties and its minutia, a 0.8m x 1.2m table, 
while not typically or generally expected, could be stretched to be within a 
range of what could be considered within the nominal range.  Likewise a table 
1.2m x 1.8m would or should still be considered within an expected or nominal 
value. To the contrary, a table 0.2m x 0.2m, for many reasons, would not be 
generally considered expected and thus not nominal, but abnormal in size for 
the intent and purposes of the standard.  
 
Remembering that there are three dimensions given (i.e. 1mx1.5mx0.8m), if we 
take your ‘exception’, then I could place a device on the ground plane as long 
as it was on a nonconducting surface.  Yet I know of no lab nor auditor that 
would accept this as a ‘nominal’ height condition for any of the standards 
mentioned.  I would not be able to reject or challenge their claim that my 
table height was not 80cm by saying, nominal is “of, being, or relating to a 
designated or theoretical size that may vary from the actual, and I don’t have 
to have a table 80cm high.”  

One might say, yes, but height matters. And they would be correct, however, the 
dimensions are together in the same frame of reference in the same sentence. So 
any exceptions to the dimensions would have to follow the same process.  The 
issue then is not uncertainty and its issues, but what is generally expected 
and accepted as a reasonable table for the intent of the standard.  
 
Remembering that standards are produced as much to make something consistent 
wherever used, then the nominal would be that which is generally consistent 
within the population that uses the standard. 
 
As to ‘bigger fish to fry’, this would be a good size fish for a lab that was 
seeking accreditation. Yes there are allowable variations, equipment 
considerations, etc that can be discussed with the accrediting organization.  
To say that because ‘nominal’ is used and because ‘shall’ is not, I can do what 
I want, is simply not the case if they want to become accredited. It is fairly 
easy and cheap to construct a nominal table of dimensions in the standards.  
There is probably more money, time and effort in trying to challenge or reject 
the assessment than to simply hire a carpenter and build one.
 
But the choice is the labs and how they wish to relate to their accreditation 
body.
 

Dennis Ward 


Director of Engineering
American Certification Body 
Certification Resource for the Wireless Industry http://www.acbcert.com
703-847-4700 fax 703-847-6888 
direct - 703-880-4841


From: Derek Walton [mailto:[email protected]] 
Sent: Tuesday, October 11, 2011 10:09 AM
To: Dennis Ward
Cc: 'Grace Lin'; 'WNya'; 'EMC-PSTC'
Subject: Re: Table Size in Emissions test

Sorry Dennis, 

you are not correct. Nominal means:

b : of, being, or relating to a designated or theoretical size that may vary 
from the actual.

This is from Websters.

As you indicate, there is NOTHING that says it has to be 1 by 1.5m

I'm sorry to be so anal about this, but it is happening too much where 
assessors are assessing to opinions and personal agendas. We must follow the 
standard. Usually there are MUCH bigger fish to fry than quibbling over 
something like this

I repeat, again, that there is NOTHING that says the table SHALL be 1 by 1.5m. 
Only then could a deficiency be written.

Sincerely,

Derek.


On 10/11/2011 11:43 AM, Dennis Ward wrote: 
Both ANSI C63.10 and ANSI C63.4, the typical standards for which ISO17025 
accreditation is used, contain the following statement, “Tabletop devices shall 
be placed on a nonconducting platform, of nominal size 1 m by 1.5 m, raised 80 
cm above the reference ground plane.

While a bit more open to variation due to size of equipment, CISPR 22 has the 
statement “Equipment intended for tabletop use shall be placed on a 
non-conductive table. The size of the table will nominally be 1,5 m ◊ 1,0 m but 
may ultimately be dependent on the horizontal dimensions of EUT.
 
So while you may challenge the accreditation organization, they are correct, 
your table does not meet the ‘nominal’ size requirements for at least the two 
standards ANSI C63.4 and C6310.
 
Other standards may also have the nominal size issue as well.
 
Thanks 
Dennis Ward 



Director of Engineering
American Certification Body 
Certification Resource for the Wireless Industry http://www.acbcert.com
703-847-4700 fax 703-847-6888 
direct - 703-880-4841
 

From: [email protected] [mailto:[email protected]] On Behalf Of Grace Lin
Sent: Tuesday, October 11, 2011 4:16 AM
To: WNya
Cc: EMC-PSTC
Subject: Re: Table Size in Emissions test


Wendy,

 

When I look for an accredited ANSI C63.4 laboratory, I expect the laboratory 
has the facility as stated in the standard, including a standard size of the 
table as defined in the standard.  For this reason, unless the accreditation 
certificate bears a restriction note, I support the auditor's comment.  

 

>From the other point of view, many manufacturers' laboratories are for 
>internal use only, including my employer's.  For this reason, the auditor may 
>be willing to accept the smaller size of the table.  The question is how to 
>determine if the laboratory is for internal use only (for testing certain type 
>of products).  An example is Alcatel-Lucent's EMC laboratory in New Jersey, 
>USA.  It opens to the general public.

 

With regards,

Grace

 

 

On Mon, Oct 10, 2011 at 7:54 PM, WNya <[email protected]> wrote:
Dear Experts,
Recently my company went through the first ISO17025 audit. We have a table 
smaller than the standard requirement of 1.5m x 1m since our products are 
small, typically 10cm x 10cm x 10cm. The height of our table was 0.8m. The 
auditor wanted us to change the table size to follow the standard.
What does it matter since we never use the extra space on the table? I do agree 
we must keep to the height requirement since the floor is a ground plane and 
thus it sets a fixed capacitance to the EUT and also controls the lengths of 
any attached cables.

Can we reject or challenge the auditor's request? Has anyone experience the 
same situation?

Sent from Wendy.Nya iPhone

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL. 
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL. 
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website:      http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules:     http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher  <[email protected]>
David Heald <[email protected]> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to