>NEBS GR63 talks about Acoustic requirement for "Equipment to be Located 
>in Telecommunications Room (attended) - 78dB (A-weighted sound power)".
>
>Question: Does this level suits for all sizes of equipment? Is the spec 
>same for 1U and 20U rack mounted equipment?
>
>Reason asking this, In a rack one could install multiple 1U system than 
>one single large system. When adding multiple system there can be noise 
>addition that could exceed the standard requirement.

There WILL be addition, RMS-wise. For a 20U rack of 1U units that are 
individually just compliant (i.e. 78 dB A), you can expect 91 dB A!

You make a good point. It's something we try to deal with in EMC 
standards. Otherwise, one gets a situation where you can put twenty 1U 
systems on shelves in a room with impunity, but if you put them in a 
rack, you cannot achieve compliance.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
I should be disillusioned, but it's not worth the effort.
But I support unbloated email http://www.asciiribbon.org/

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@socal.rr.com>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to