Brian,

Referring first to the IEV (IEC 60050) we get these related definitions:


IEV number 195-01-13 <http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> functional earthing,
functional grounding (US)  <http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif>  
earthing a point or points in a system or in an installation or in equipment,
for purposes other than electrical safety 


IEV number 195-02-15 <http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> functional earthing conductor,
functional grounding conductor (US)  <h
tp://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif>  
earthing conductor provided for functional earthing 
<http://www.electropedia.org/icons/ecblank.gif> 


IEV number 195-02-16 <http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> functional bonding conductor 
<http://www.electropedia.org/icons/ecblank.gif> 
<http://www.electropedia.org/icons/ecblank.gif> conductor provided for
functional-equipotential-bonding  <http
//www.electropedia.org/icons/ecblank.gif> 


IEV number 195-02-17 <http://www.electropedia.org/icons/ecblank.gif> 
protective earthing and functional earthing conductor, protective grounding
and functional grounding conductor (US)
conductor combining the functions of both a protective earthing conductor and
a functional earthing conductor


>From IEC 60204-1-05 we get:
3.27
functional bonding
equipotential bonding necessary for proper functioning of electrical equipment
3.43
protective bonding
equipotential bonding for protection against electric shock
NOTE Measures for protection against electric shock can also reduce the risk
of burns or fire.
3.44
protective bonding circuit
protective conductors and conductive parts connected together to provide
protection against
electric shock in the event of an insulation failure
3.45
protective conductor
conductor required for protective bonding by some measures for protection
against electric
shock for electrically connecting any of the following parts:
– exposed conductive parts;
– extraneous conductive parts;
– main earthing terminal (PE)
[IEV 826-13-22, modified]


8 Equipotential bonding
8.1 General
This Clause provides requirements for both protective bonding and functional
bonding. Figure 2
illustrates those concepts.


Protective bonding is a basic provision for fault protection to enable
protection of persons
against electric shock from indirect contact (see 6.3.3 and 8.2).


The objective of functional bonding (see 8.3) is to minimize:



        – the consequence of an insulation failure which could affect the 
operation
of the machine;
        – the consequences of electrical disturbances to sensitive electrical
equipment which could
        affect the operation of the machine.

        
        

Normally functional bonding is achieved by connection to the protective
bonding circuit, but
where the level of electrical disturbances on the protective bonding circuit
is not sufficiently low
for proper functioning of electrical equipment, it may be necessary to connect
the functional
bonding circuit to a separate functional earthing conductor (see Figure 2).

I've made Figure 2 available at http://
ww.dougnix.net/Life/IEC_60204-1_Figure_2.html

Based on all the forgoing, I would define the two as follows:

Protective earth,and therefore symbol 5019, is the system used to prevent
shock and maintain touch voltages on exposed conductive metal parts of the
product to non-hazardous levels. The system also provides a means to ensure
that protective devices will open the supply circuits to the product in the
event that a fault occurs between a phase conductor and the chassis or a
conductive metal part of the product.

Functional earth and therefore symbol 5017, is the system used to provide an
equipotential reference point for the electrical system EXCLUDING the safety
functionality provided by the Protective Earth system. This could be used as a
reference point for instrumentation (although this is more commonly done with
a "noiseless earth" connection), or a common for any other non-safety related
electrical function. I would argue that the Neutral Conductor represents a
Functional Earth application, as it is the common reference in systems that
use it, and it does not have a safety function. 

Referring to Keith Armstrong and Tim Williams book "EMC for Systems and
Installations", p.102/103:



        5. 1. 1. 1 Safety earth 
        The purpose of the safety earth is to guarantee personnel safety under 
fault
conditions. The lEE Wiring Regulations (BS 7671, [114]) define "earthing" as 
        
        
        Connection of the exposed conductive parts of an installation to the 
main
earthing terminal of that installation. 

        
        

        Earthing ensures the provision of a low impedance path in which current 
may
flow under fault conditions. Exposed conductive parts are those conductive
parts of equipment which may be touched and which may become live in the case
of a fault. The earthing connection prevents such live parts from reaching a
hazardous voltage. Equipotential bonding, in this context, is a means of
electrical connection intended to maintain various exposed and extraneous
conductive parts at substantially the same potential under both operational
and fault conditions. The protective conductor (typically colour coded
green-and-yellow) provides this means and also connects the conductive parts
to the installation's main earthing terminal. The prospective touch voltage
within the installation is then the product of the impedance of the protective
conductor and the earth fault current. 

        
        
        Equipotential bonding therefore creates an equipotential zone within 
which
exposed and extraneous conductive parts are maintained at "substantially" the
same potential. It is worth noting that although the voltages within such a
zone may be safe, they are not necessarily, and not even usually, zero.
Continuous currents from various sources, including equipment earth leakage,
are likely to be flowing, even in a "healthy" circuit. Allowable earth leakage
levels from individual items of equipment are covered in section 4.4.1.1 on
page 97. An "equipotential" zone may protect people but may not protect
equipment or wiring. Moreover, within a large installation there may be more
than one "equipotential" zone for safety purposes and the voltages existing
between them may well be large and undefined; special precautions need to be
taken for signal wiring (such as local area networks) that may cross such
zones, to prevent them importing potentially hazardous voltages. 
        
        
        Protection against electric shock is typically provided by earthing in
conjunction with automatic disconnection of the supply. For this purpose, it
is vital to co-ordinate selection of the protective device (for instance,
fuse, circuit breaker or RCD) with the installation's earth fault impedance,
to ensure that disconnection occurs sufficiently rapidly to prevent the touch
voltage from rising high enough to cause a shock. The sizing and hence
resistance of the earth protective conductor will therefore be determined
largely by the prospective fault current available from the rest of the
system. In the case of protective multiple earthing (PME), the protective
conductors may take substantial continuous currents, even when the supply is
off, as a result of circulating currents in the bonding network, and therefore
may need over-rating. Since the concern is currents at low frequencies, it is
resistance rather than inductance which determines the conductor impedance;
this is not the case for high-frequency earths, as we see later. 
        
        5.1.1.2 Functional earth 
        In order for an electrical circuit to interface correctly with other 
equipment, there must be a means
both of relating voltages In one equipment to those in another, and of
preventing adjacent but galvanically separate circuits from floating. 
        
        
        This is the purpose of the functional earth and it must be 
distinguished from
the safety protective earth. Earth conductors which are used for functional
purposes only need have no requirements for sizing according to safety but
should be coloured cream (according to BS767l) to identify them. Even so,
because of the threat of circulating currents and potential differences
between earthing zones, there may be other practical constraints on the
widespread use of functional earthing on large systems. 
        
        
        Signal circuits of equipment should normally be specified for a maximum
common mode voltage, which will be the voltage that appears between different
parts of a functionally-earthed system. If this voltage is likely to be
exceeded, implementation of a Common Bonding Network (CBN, see 5.1.3.3) in the
system is recommended. If this is impractical or inadequate, isolated circuit
interfaces are the normal solution. 
        
        

I hope that helps!

-- 
Doug Nix, A.Sc.T.
IEEE PSES Toronto Chapter 
Toronto Section, Ontario, Canada

[email protected] 
mobile (519) 729-5704
fax (519) 653-1318

Find me LinkedIn at http://www.linkedin.com/in/dougnix



On 22-Sep-09, at 2:10 PM, Kunde, Brian wrote:


        Functional Earth Terminals


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to