Hi Jim:

> Returning to the 120Vdc limit in UL1703 and other standards, a quick look at 
> 61201 says that 120Vdc would cause at least tetanization in most situations, 
> even in dry conditions.

DC does not cause tetanization.  Only AC within
a specific frequency range causes tetanization.

IEC 61202, 2nd, sub-clause 4.1 states:

This specification addresses the following physiological effects:
– startle reaction from current;
– strong involuntary muscular reaction (such as inability to let-go from an 
electrode for a.c.);
– ventricular fibrillation.


Best regards,
Rich













---- Jim Eichner <[email protected]> wrote: 
> The horizontal standards on this topic should be required reading for anyone 
> in the safety compliance field.  Only in the last few years have I become 
> familiar with the details contained in IEC 61201 and IEC 60479, and it not 
> only explained the basis of the type of discrepancy that started this thread, 
> but it made me realize how uninformed some standards writing committees may 
> have been in the past. Admittedly even these horizontal documents have 
> undergone major revisions in the last 5 years, and it appears to be a topic 
> where we still have much to learn (except as noted in a previous post, that 
> electricity is rarely without hazard!)
> 
> To establish a safe touch voltage limit requires analysis and assumptions 
> around the following parameters:
> 
> - area of contact (fingertip, whole hand, large part of the body, etc.)
> - skin condition (dry, wet, salt water wet, immersed)
> - path the current will take (hand to hand, one hand to both feet, etc.)
> - condition you are trying to protect against (startle reaction, tetanization 
> (inability to let go), and ventricular fibrillation are all used as the basis 
> for touch voltages in various well established standards)
> - who you are trying to protect: healthy adults, surgical patients, small 
> children, infirm elderly people, etc.
> - the statistical level you are trying to achieve (a given current may be 
> safe for X% of the healthy adult population and not for the rest - roll the 
> dice anyone?)
> 
> So the symptom is that even very well established standards have different 
> voltage limits, but the underlying problem may be lack of awareness of these 
> factors and the need to analyze the types of equipment and users involved and 
> make informed decisions on all of these factors. I believe it is also 
> important for a standard to state clearly what assumptions were made - what 
> the basis of the touch voltage limits is.  A sample statement, as un-nerving 
> as it may seem at first, would be something along the lines of "The touch 
> voltage limits in this standard will protect 80% of the population against 
> tetanization, under dry conditions, when the live part is contacted by an 
> area no larger than the hand, and the current path is from one hand to either 
> or both feet".  It could go further and state what outcomes can be expected 
> outside these boundaries: hand to hand current or wet conditions may cause 
> V-Fib in some portion of the population, etc.  If nothing else, it would make 
> desi!
 gn!
>  ers and Certifiers think a bit more before blindly accepting touch voltage 
> limits.
> 
> By the way, the approaches that I am proposing here are being followed by the 
> authors of IEC 62477 (TC22, PT5) which is the future "group safety function" 
> (ie nearly horizontal) standard for safety of all power conversion equipment. 
>  It is to that group that I owe my relatively new understanding of all this.  
> The users of that standard will be the authors of product standards, who will 
> be given the choice of either accepting the numbers in 62477 (which will 
> clearly state the basis for those numbers) or using its approaches for 
> determining other limits based on different assumption sets.
> 
> Returning to the 120Vdc limit in UL1703 and other standards, a quick look at 
> 61201 says that 120Vdc would cause at least tetanization in most situations, 
> even in dry conditions.  Only very small contact areas would result in a less 
> severe situation.  Under wet conditions the curves are a little different 
> (not as much as you might expect) and a hazard arises sooner as you increase 
> contact area or voltage.  I would not call 120Vdc safe on an outdoor product 
> with metal surfaces large enough to contact with your whole hand, with your 
> feet on wet ground or on a grounded metal panel mounting bracket, and in fact 
> the very existence of a Class 2 designation for solar panels was called into 
> question at the last IEC TC82 (PV) meeting I was at.
> 
> Jim Eichner
> Compliance Engineering Manager
> Xantrex Technology Inc.
> e-mail: [email protected]
> web:  www.xantrex.com 
> 
> Confidentiality Notice: This e-mail message, including any attachments, is 
> for the sole use of the intended recipient(s) and may contain confidential 
> and privileged information.  Any unauthorized review, use, disclosure or 
> distribution is prohibited.  If you are not the intended recipient, please 
> contact the sender by reply e-mail and destroy all copies of the original 
> message
> 
> 
> 
>  
> 
> -----Original Message-----
> From: [email protected] [mailto:[email protected]] On Behalf Of Haynes, Tim 
> (SELEX GALILEO, UK)
> Sent: Friday, July 31, 2009 4:50 AM
> To: John Woodgate; [email protected]
> Subject: RE: "safe" voltage differences between UL 1703 and IEC 61140
> 
> Hi All and John!
> 
> Back to basics (as I read them) and a light hearted review of published
> information.
> 
> ICNIRP and a few other sources put the threshold of perception as 1mA
> a.c.
> 
> Other sources give the resistance of a person as 2kOhms.
> 
> This puts the voltage associated with the perception of an electric
> shock at 2V a.c. Death can occur (according to some documents) with a.c.
> current above 9mA - that would be 18Va.c. for a 2kOhm person
> 
> Taking a step further, the resistance of a person that has lost the
> normal layers of skin is very low - so a 2V a.c. source connected to two
> cheese graters could be lethal!
> 
> Of course 2V a.c. has never been safe if the current is unlimited - it
> might not shock you, but it can give you a shock to find that the low
> voltage source has caused a fire.
> 
> 1.4V d.c (a NiCad cell) put a good burn on the inside right of my right
> thigh when I mistakenly put the car keys in the same pocket as the spare
> re-chargables for my camera. That gave me a shock!
> 
> Many years ago, I remember being told that an old lady died from a shock
> caused by a 9v "radio" battery - but I cannot vouch for the truth of
> this tale.
> 
> Seriously, there is a risk with electricity that never quite goes away.
> The lower the voltage, the greater is the chance that a person will
> survive the shock. Given the range of resistance that exists in people,
> it would be a very bad day if someone with 2k resistance came into
> contact with 18V and died as a result.
> 
> However, if you want to have a safe product, it is probably not worth
> arguing over what voltage is safe, it is better to prevent access to any
> voltage - just in case the person has been grating cheese.
> 
> There are some serious thoughts in the above if you look for them.
> 
> Have a good week end
> Regards
> Tim
> 
> ************************
> SELEX Sensors and Airborne Systems Limited
> Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14 
> 3EL
> A company registered in England & Wales.  Company no. 02426132
> ********************************************************************
> This email and any attachments are confidential to the intended
> recipient and may also be privileged. If you are not the intended
> recipient please delete it from your system and notify the sender.
> You should not copy it or use it for any purpose nor disclose or
> distribute its contents to any other person.
> ********************************************************************
> 
> -
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> <[email protected]>
> 
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieeecommunities.org/emc-pstc
> Graphics (in well-used formats), large files, etc. can be posted to that URL.
> 
> Website:  http://www.ieee-pses.org/
> Instructions:  http://listserv.ieee.org/request/user-guide.html
> List rules: http://www.ieee-pses.org/listrules.html
> 
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
> 
> For policy questions, send mail to:
> Jim Bacher:  <[email protected]>
> David Heald: <[email protected]>
> 
> -
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> <[email protected]>
> 
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieeecommunities.org/emc-pstc
> Graphics (in well-used formats), large files, etc. can be posted to that URL.
> 
> Website:  http://www.ieee-pses.org/
> Instructions:  http://listserv.ieee.org/request/user-guide.html
> List rules: http://www.ieee-pses.org/listrules.html
> 
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
> 
> For policy questions, send mail to:
> Jim Bacher:  <[email protected]>
> David Heald: <[email protected]>

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to