The horizontal standards on this topic should be required reading for anyone
in the safety compliance field.  Only in the last few years have I become
familiar with the details contained in IEC 61201 and IEC 60479, and it not
only explained the basis of the type of discrepancy that started this thread,
but it made me realize how uninformed some standards writing committees may
have been in the past. Admittedly even these horizontal documents have
undergone major revisions in the last 5 years, and it appears to be a topic
where we still have much to learn (except as noted in a previous post, that
electricity is rarely without hazard!)

To establish a safe touch voltage limit requires analysis and assumptions
around the following parameters:

- area of contact (fingertip, whole hand, large part of the body, etc.)
- skin condition (dry, wet, salt water wet, immersed)
- path the current will take (hand to hand, one hand to both feet, etc.)
- condition you are trying to protect against (startle reaction, tetanization
(inability to let go), and ventricular fibrillation are all used as the basis
for touch voltages in various well established standards)
- who you are trying to protect: healthy adults, surgical patients, small
children, infirm elderly people, etc.
- the statistical level you are trying to achieve (a given current may be safe
for X% of the healthy adult population and not for the rest - roll the dice
anyone?)

So the symptom is that even very well established standards have different
voltage limits, but the underlying problem may be lack of awareness of these
factors and the need to analyze the types of equipment and users involved and
make informed decisions on all of these factors. I believe it is also
important for a standard to state clearly what assumptions were made - what
the basis of the touch voltage limits is.  A sample statement, as un-nerving
as it may seem at first, would be something along the lines of "The touch
voltage limits in this standard will protect 80% of the population against
tetanization, under dry conditions, when the live part is contacted by an area
no larger than the hand, and the current path is from one hand to either or
both feet".  It could go further and state what outcomes can be expected
outside these boundaries: hand to hand current or wet conditions may cause
V-Fib in some portion of the population, etc.  If nothing else, it would make
design!
 ers and Certifiers think a bit more before blindly accepting touch voltage
limits.

By the way, the approaches that I am proposing here are being followed by the
authors of IEC 62477 (TC22, PT5) which is the future "group safety function"
(ie nearly horizontal) standard for safety of all power conversion equipment. 
It is to that group that I owe my relatively new understanding of all this. 
The users of that standard will be the authors of product standards, who will
be given the choice of either accepting the numbers in 62477 (which will
clearly state the basis for those numbers) or using its approaches for
determining other limits based on different assumption sets.

Returning to the 120Vdc limit in UL1703 and other standards, a quick look at
61201 says that 120Vdc would cause at least tetanization in most situations,
even in dry conditions.  Only very small contact areas would result in a less
severe situation.  Under wet conditions the curves are a little different (not
as much as you might expect) and a hazard arises sooner as you increase
contact area or voltage.  I would not call 120Vdc safe on an outdoor product
with metal surfaces large enough to contact with your whole hand, with your
feet on wet ground or on a grounded metal panel mounting bracket, and in fact
the very existence of a Class 2 designation for solar panels was called into
question at the last IEC TC82 (PV) meeting I was at.

Jim Eichner
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: [email protected]
web:  www.xantrex.com 

Confidentiality Notice: This e-mail message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information.  Any unauthorized review, use, disclosure or
distribution is prohibited.  If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message



 


From: [email protected] [mailto:[email protected]] On Behalf Of Haynes, Tim
(SELEX GALILEO, UK)
Sent: Friday, July 31, 2009 4:50 AM
To: John Woodgate; [email protected]
Subject: RE: "safe" voltage differences between UL 1703 and IEC 61140

Hi All and John!

Back to basics (as I read them) and a light hearted review of published
information.

ICNIRP and a few other sources put the threshold of perception as 1mA
a.c.

Other sources give the resistance of a person as 2kOhms.

This puts the voltage associated with the perception of an electric
shock at 2V a.c. Death can occur (according to some documents) with a.c.
current above 9mA - that would be 18Va.c. for a 2kOhm person

Taking a step further, the resistance of a person that has lost the
normal layers of skin is very low - so a 2V a.c. source connected to two
cheese graters could be lethal!

Of course 2V a.c. has never been safe if the current is unlimited - it
might not shock you, but it can give you a shock to find that the low
voltage source has caused a fire.

1.4V d.c (a NiCad cell) put a good burn on the inside right of my right
thigh when I mistakenly put the car keys in the same pocket as the spare
re-chargables for my camera. That gave me a shock!

Many years ago, I remember being told that an old lady died from a shock
caused by a 9v "radio" battery - but I cannot vouch for the truth of
this tale.

Seriously, there is a risk with electricity that never quite goes away.
The lower the voltage, the greater is the chance that a person will
survive the shock. Given the range of resistance that exists in people,
it would be a very bad day if someone with 2k resistance came into
contact with 18V and died as a result.

However, if you want to have a safe product, it is probably not worth
arguing over what voltage is safe, it is better to prevent access to any
voltage - just in case the person has been grating cheese.

There are some serious thoughts in the above if you look for them.

Have a good week end
Regards
Tim

************************
SELEX Sensors and Airborne Systems Limited
Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14
3EL
A company registered in England & Wales.  Company no. 02426132
********************************************************************
This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.
********************************************************************

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to