QUOTE from Don Borowski: "A number of capacitors in the capacitor bank 
were later found to be bulging from overheating. The equipment to monitor 
the condition of the capacitors (by monitoring electrical parameters) did 
not catch the developing problem before the explosion. "
 
Bulging capacitors are typically a sign of an overvoltage condition caused by 
transients (even transients in the micro-second range).  Today's modern 4 
quadrant regenerative drives can and do cause bus pump-up to occur 
in regeneration mode during which overvoltage transients can be induced on the 
bus.  Inadequate filtering/transient suppression of these transients can be 
damaging to voltage sensitive devices such as capacitors on the bus.  
 
Gary Stuyvenberg
Senior EMC Consultant
Thompson Consulting
Wind Lake, WI  USA
 
 

--- On Tue, 1/17/12, [email protected] <[email protected]> wrote:


From: [email protected] <[email protected]>
Subject: Re: cruise liner harmonic interference?
To: "John Woodgate" <[email protected]>
Cc: [email protected], [email protected]
Date: Tuesday, January 17, 2012, 1:34 PM


The Queen Mary 2 was totally without power for at least an hour when a 
capacitor bank exploded, blowing the reinforced steel door off of a power 
cabinet (like those used in "enclosed" power substations). The capacitors 
are used to filter harmonics from the electronic drive for the electric 
propulsion motors whose power can total over 100 MW. The ship was in open 
water and so was in no immediate danger. It finally got under way again a 
few hours later at reduced power.

The cause of the problem was not EMC as such, but was definitely related 
to the electrical system. A number of capacitors in the capacitor bank 
were later found to be bulging from overheating. The equipment to monitor 
the condition of the capacitors (by monitoring electrical parameters) did 
not catch the developing problem before the explosion. The electrical 
system was unable to reconfigure itself to maintain even partial power.

So yes, I could believe that a ship could get into trouble quickly if 
there were a major electrical failure. If this turns out to be the cause 
for the Concordia disaster, I am surprised that international standards 
had not been revised and enforced in light of the power failure on the 
Queen Mary 2.

Donald Borowski
EMC Engineer
Schweitzer Engineering Labs
Pullman, WA, USA




From:   John Woodgate <[email protected]>
To:     [email protected]
Date:   01/17/2012 11:05 AM
Subject:        Re: cruise liner harmonic interference?
Sent by:        [email protected]



In message 
<ca7a2231c689d14c9df8bc211ade9f03082...@dcexchmb100vm.tennant.tco.corp>, 
dated Tue, 17 Jan 2012, "Bender, Curtis" <[email protected]> 
writes:

>An interesting (but sad) article for the EMC and PSTC interests.
>
>http://www.guardian.co.uk/world/2012/jan/14/italian-cruise-disaster-caus
>e-power
>

This must be pure speculation. Furthermore:

According to this scenario, a power surge or "harmonic interference" 
could have caused a malfunction in the generators feeding the ship's six 
diesel-electric engines, while back-up systems failed to provide power 
with sufficient speed. This would have caused the ship to lose 
navigational power and steering control and to veer off course.

..is typical ignorant journalistic mumbo-jumbo.  Losing power would 
cause 'reset to default' of all systems, which doesn't sound like 'veer 
off course' to me. In any case, these critical systems are subject to 
redundancy requirements. A total power failure must have infinitesimal 
probability.

>I?m sure it?s possible but how probable is it to lose ALL power long 
>enough to run a ground? Seems to me that should have been one of the 
>first items covered in a Risk Assessment.

>Are EMC test standards typically followed for cruise liners

IEC TC80 deals with ship electrics and electronics, but the IMO has a 
great influence and is often accuse of excessive conservatism.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
Some people who are peeling the finch of the financial crisis are thinking 
of
biting a rook.

-

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to