Doug-

I don't see the need for a fuse in series with a neutral-to-ground MOV. 
The MOV should never get to the point where it is conducting on the peaks 
of the normal voltage waveform to cause thermal runaway, since this 
voltage is so low (I×R drop in the wire due to the load).

If a fuse is still wanted or needed to cover the case of miswiring (hot 
and neutral reversed), a blown fuse could be monitored. Assume correct 
wiring. Run a rather high value resistor from the hot wire to the junction 
of the fuse and MOV. Then normally there will be voltage across the 
resistor which will disappear with a blown fuse. Or no voltage across the 
MOV normally, but voltage will appear with a blown fuse.

Don



From:   [email protected]
To:     [email protected]
Cc:     "emc-pstc" <[email protected]>
Date:   09/24/2012 07:55 AM
Subject:        Re: MOV failure detection



Don,

Voltage sensing the fuse is useful on any line which has enough voltage 
with respect to earth.  The MOV tied to the neutral is much more difficult 
to detect in this way.  However, I would venture to say that this MOV is 
not subjected to so many impulses as the other. 

The line-to-line MOV presents a new problem, if present.  I have seen 
phase monitors used which are optocouplers using neon lamp.  This can 
provide isolation to your monitoring circuits.


Doug

Douglas E Powell
Independent Compliance Consultant
http://www.linkedin.com/in/dougp01

 
http://www.linkedin.com/in/dougp01

-----Original Message-----
From: [email protected]
Date: Mon, 24 Sep 2012 07:23:36 
To: <[email protected]>
Cc: <[email protected]>
Subject: Re: MOV failure detection

In normal use, the way MOVs wear out is that the conduction voltage 
decreases as they continue to absorb the energy from voltage transients. 
They go over the cliff when the conduction voltage drops to the peaks of 
the power line voltage, at which point they are absorbing energy 
continuously. If nothing is done, the MOVs will get very hot and let the 
smoke out, quite possibly including the smoke contained in the contents of 

the rest of the room.

The way to protect against this failure mode is to put a fuse in series 
with the MOV. If this is done, there are two possible indicators that can 
be used to signal whether transient protection is taking place. Quite 
often a green LED will be lit using the voltage across the MOV to indicate 

normal operation and transient protection. The alternative is to use a red 

LED powered by the voltage across the fuse. It will stay off until there 
is a fault that blows the fuse, and then comes on indicating loss of 
protection.

An MOV can fail open, but most often that happens when there is a 
spectacular event like a lightning strike. This may blow the fuse, or 
possibly cause the device containing the MOV to explode, in which case 
there is a fairly clear failure indication of a different sort.

Donald Borowski
EMC Compliance Engineer
Schweitzer Engineering Labs
Pullman, WA, USA



From:   [email protected]
To:     [email protected]
Date:   09/23/2012 08:31 AM
Subject:        MOV failure detection
Sent by:        [email protected]



Aside from all the regulatory issues of leakage current and nasty failure 
modes of MOVs.  What methods have been used to detect a failed transient 
suppression device in equipment?  Or, is there some expectation the 
devices will survive a warranty period and that alone is good enough? 

Seems like any detection schemes would also have a series of regulatory 
issues and be a significant cost adder to the product.


Doug

Douglas E Powell
Independent Compliance Consultant
http://www.linkedin.com/in/dougp01


http://www.linkedin.com/in/dougp01

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to