A few points, which may, or may not, be useful:

 

1)       Annex E is only informative, not normative

2)       From what you have described, the equipment is operated in an
uncontrolled environment, but is not opened in that environment during
installation or maintenance (at least the PCB, which is the bit you are
concerned about).  We aren't worried about deposition on the outside, the
enclosure, only on the PCB and other components inside.

3)       You then need to know the pollution degree of the macro
environment, basically whether or not it's in a dirty dusty damp environment
or whatever.

4)       That together takes you into the table, and you can see where it
comes out, it might be that X5 or X6 would do.

5)       The IP figures don't make much sense to me, because it seems odd to
only consider the water ingress value, and not also bother with the solid
objects one.  Surely dust ingress is as important, and maybe more important,
than just moisture ingress?

 

John C

 

  _____  

From: Ian White (SXS UK) [mailto:[email protected]] 
Sent: 31 October 2012 14:49
To: [email protected]
Subject: [PSES] LVD Standard EN61010-1:2010 and Annex E

 

 

Can l have your comments on this please.

 

 

EN61010-1:2010 Annex E deals with the guidelines for the reduction of
pollution degrees due to the micro-environment created by the enclosure.  

 

Is it really saying that any product in a uncontrolled environment must have
a IPX7 or IPX8 enclosure rating before the reduction can take place. See
table below :

 


7

Immersion up to 1 m

Ingress of water in harmful quantity shall not be possible when the
enclosure is immersed in water under defined conditions of pressure and time
(up to 1 m of submersion).

Test duration: 30 minutes

Immersion at depth of 1m


8

Immersion beyond 1 m

The equipment is suitable for continuous immersion in water under conditions
which shall be specified by the manufacturer. Normally, this will mean that
the equipment is hermetically sealed. However, with certain types of
equipment, it can mean that water can enter but only in such a manner that
it produces no harmful effects.

Test duration: continuous immersion in water

Depth specified by manufacturer

 

 

 

As l have read Annex E  if a controller (which has a IP65 facia keypad but
IP4X case) which is designed to be fitted into a panel would really require
a IPX7 or IPX8 case (if a pollution reduction was allowed to take place at
the pcb level) as the controller enclosure (not the pcb) would be exposed to
uncontrolled environmental conditions during installation or maintenance. 

 

This does seem a little extreme as these times are very small compared to
the life of the controller and the actual pcb will never be exposed.

 

Do l understand Annex E correctly ?

 

 

Thanks

 

Ian White

Compliance and Reliability

 

 

 

 


_____________________________________________________________________
Spirax-Sarco Engineering Plc. This e-mail has been scanned for viruses by
Verizon Business Internet Managed Scanning Services - powered by
MessageLabs. For further information visit http://www.verizonbusiness.com/uk

-
----------------------------------------------------------------


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to