Something to keep in mind,

Peak Voltages (spikes, impulses, flyback, laser ignition, etc.) are more a
concern for clearances than for creepage.  Committees build creepage tables
in slightly different ways and they sometimes ignore the relationships of
Vrms, Vpk and Vdc which are often related by 1.414 and so on.  On the
clearance tables this is a somewhat less common practice, especially in
secondary circuits where interpolation is allowed.  One of the main keys is
if you make allowance for high peak voltage values in clearance, the rule
"creepage cannot be less than clearance" applies.  On occasion, creepage
calculations will come in lower than clearance in which case the creepage
number must be automatically bumped up to match the clearance.


thanks, -doug

Douglas E Powell
http://www.linkedin.com/in/dougp01


On Mon, May 12, 2014 at 11:45 AM, Brian Oconnell
<[email protected]>wrote:

> The issue with some 60664 tables is that it is (for 0 to 2km) based on
> Paschen's Law, which is for a simple homogenous e-field. So creepage via
> RMS is an incomplete analysis.
>
> As others have stated, spacing should be determined by both peak and RMS.
> And because too many do not measure WV correctly, I strongly suggest
> reading papers and articles by P. Perkins and R. Nute on this subject, and
> "The physical fundamentals of low-voltage insulation co-ordination" by
> Klaus Stimper.
>
> In a very nutty shell, you need to determine the following for the
> intended end-use environment:
>  - OV category
>  - CTI of materials
>  - pollution degree
>  - atmospheric chemistry
>  - frequency-based di-electric heating
>  - WV for the complete range of rated operating conditions
>
> Have rejected more than one component mfr's CB reports due to incorrect
> interpretations of IEC60664 and calculations of 'RMS' (am looking at you
> people in NRTLs/SCCs/NBs). Finally, the OP indicated that "Creepage is
> based on the RMS value of the voltage so is based on 1120 V", which
> indicates a reference a particular safety standard. What does that standard
> say about WV measurements for the determination of spacing and test
> voltages ?
>
> Brian
>
> ----- Original Message -----
> From: ce-test, qualified testing bv - Gert Gremmen
> Sent: 05/12/14 03:20 PM
> To: [email protected]
> Subject: [PSES] Creepage and RMS
>
> I have a question on creepage distances.
> A product creates a saw tooth High voltage
> of 2000 Vpeak  The VRMS measured on the scope
> on a full period equals 1120 V
>
> Creepage is based on the RMS value of the voltage
> so is based on 1120 V.
>
> Now the frequency of the sawtooth is 3 Hz.
> Should I still consider the RMS value,
> and at what frequency should I consider this
> as a DC value in regard to creepage....
>
> Anyone aware of the IEC 60664 standard in respect
> to low frequency signals ??
>
> Regards,
>
> Ing.  Gert Gremmen, BSc
>
> -
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website:  http://www.ieee-pses.org/
> Instructions:  http://www.ieee-pses.org/list.html (including how to
> unsubscribe)
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher:  <[email protected]>
> David Heald: <[email protected]>
>



-- 

Douglas E Powell
970-646-3732
[email protected]
Skype: doug.powell52
http://www.linkedin.com/in/dougp01

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to