Actually I need to meet the standard for outdoor enclosures, UL 60950-22, and 
clause 6.1 refers back to UL 60950-1 clause 2.2.2 and 2.2.3.  The difference is 
the voltage limits are reduced, due to contact resistance of the body being 
reduced when subjected to wet locations.  The clause states the voltage 
difference under a single fault must not exceed 30 V ac, without any mention of 
current.  Am I reading this correctly?

John Cochran
STRONGARM Designs
425 Caredean Drive
Horsham, PA 19044
PHONE: 215-443-3400 X193
FAX: 215-443-3002

From: Richard Nute [mailto:[email protected]]
Sent: Friday, September 05, 2014 8:05 PM
To: John Cochran; [email protected]
Subject: Re: [PSES] UL 60950-1 clause 2.2.3



Hi John:


Nothing wrong.  When the ground is opened, you get
about half the mains on the (formerly) grounded
parts.  All equipment does this, including two-
wire equipment.  Even a three-wire power cord does
this!

The voltage is due to a capacitive voltage divider,
line-chassis-neutral.  The capacitances are in the
line filter and the strays due to the wiring.

The key is the current.  It is (or should be) less
than that specified in the standard.  This is
"touch" nee "leakage" current.  Measure the current
to ground and you will find any where from 0.5 mA
to 5 mA.

When you touch the chassis, the voltage drops to
about 20 volts or less, and you may feel a tingle.

The source impedance (to mains) is about 200 k
(capacitive reactance), maybe more, maybe less,
depending on the equipment.


Best regards,
Rich

On 9/5/2014 12:49 PM, John Cochran wrote:
From: John Cochran
Sent: Friday, September 05, 2014 3:47 PM
To: '[email protected]<mailto:[email protected]>'
Subject: UL 60950-1 clause 2.2.3

I am doing compliance testing on an outdoor computer/display and am having 
problems with complying with clause 2.2.3 of UL 60950-1 and clause 6.2  of UL 
60950-22.  When the earth ground is disconnected, there is an AC potential on 
the chassis ground that is ½ of the line voltage.  At 240VAC, there is 120VAC 
on the ground.  Since everything is grounded in the system and it is in an 
aluminum enclosure, I have this potential everywhere.  I cannot find an open 
frame AC power supply that does not do the same thing.  What is it that I am 
doing wrong.  The UL 60950-22 standard says the maximum AC voltage that is 
acceptable is 15VAC.

John Cochran
425 Caredean Drive
Horsham, PA 19044
PHONE: 215-443-3400 X219
FAX: 215-443-3002




-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to