In message
<b87b3216c599564e9071daf63e06e7491eab4b8...@exchange.wonderwarene.com>,
dated Sun, 7 Sep 2014, John Cochran <[email protected]> writes:
Actually I need to meet the standard for outdoor enclosures, UL
60950-22, and clause 6.1 refers back to UL 60950-1 clause 2.2.2 and
2.2.3. The difference is the voltage limits are reduced, due to
contact resistance of the body being reduced when subjected to wet
locations. The clause states the voltage difference under a single
fault must not exceed 30 V ac, without any mention of current. Am I
reading this correctly?
Probably correctly, but not completely. The missing piece is how the
voltage is measured. If the hazard is 'touch current', then 5.1 of
60950-1 applies. However, 6.1 of 60950-22 doesn't seem to recognize that
the voltage present on user-accessible conductive parts may come from a
high-impedance source, so that it is the touch current and not the
voltage that matters.
Maybe Mr. Nute can throw more light on this.
--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
Quid faciamus nisi sit?
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion
list. To post a message to the list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>