Unless specifically stated in the safety standard used to assess the end-use 
equipment, dunno. Might want to look at NFPA70E article 130.

Due to the calculations that must be performed in order properly label 
equipment, gonna guess that the 'generic' warnings/cautions and symbols could 
be applied at factory, with specific data at installation.

Brian

From: Nyffenegger, Dave [mailto:[email protected]] 
Sent: Wednesday, December 17, 2014 11:34 AM
To: [email protected]
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

So I’m looking at the new NFPA 79 2015 (which you can view on-line for free 
now) and they have added 16.2.3 Electrical equipment for industrial machines 
such as control panels and disconnects shall be marked according to ANSI Z535.4 
to warn of shock and arc flash hazards.  I don’t have a copy of the ANSI 
standard.    NFPA 79 doesn’t say anything further regarding applying the label 
in the field or in the factory.    Do we assume this implies field labeling as 
it’s been or does this mean we are now to apply the arc flash labels in the 
factory?  I’m guessing the ANSI standard only covers the label and says nothing 
about when the label is applied.

-Dave

From: Scott Aldous [mailto:[email protected]] 
Sent: Tuesday, November 25, 2014 11:43 AM
To: [email protected]
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

FYI - Regarding the SCCR, it's really not about the interrupt rating of 
overcurrent protection devices. It relates to the ability of the equipment to 
withstand the fault currents that overcurrent devices would let through in a 
short circuit event. Looking through the supplement in UL 508A is instructive. 
If you try to evaluate through the "weakest link" method rather than testing, 
values are assigned to components commonly found in switchgear, including bus 
bars. If you have overcurrent protection that is current lmiting, it helps 
reduce the required withstand rating of components downstream, but this is 
dependent on the extent of current limiting rather than interrupt rating.

On Tue, Nov 25, 2014 at 8:33 AM, Ted Eckert <[email protected]> wrote:
Hello Brian,

The role the enclosure plays in arc flash protection may be less than you would 
expect. The concern about arc flash isn't for normal operation of the 
equipment. Arc flash and arc blasts are considered an issue for the servicing 
of equipment. The concern is that service personnel may accidentally create a 
short circuit between two phases or a phase and ground. This could occur due to 
improperly de-energizing circuits or when a metal tool or part is accidentally 
placed such that it creates a short circuit.

NFPA 70E requires that the arc flash boundary be calculated, although it is 
assumed to be 4 feet (1.2 meters) for typical small equipment rated 250 V or 
less connected to a branch circuit breaker. The boundary will be greater 
depending on the rating of the circuits overcurrent protector. NFPA 70E 
requires that untrained and unprotected personnel must remain outside of that 
boundary during the service of equipment. Personnel inside of that boundary 
must be properly trained and they must be wearing the correct PPE based on the 
arc flash hazard risk. Since this is an issue during the servicing of equipment 
when doors are open and covers are off, the enclosure provides no protection. 
The arc flash rules just require marking indicating the hazard so that service 
personnel can take the proper precautions.

Field wired equipment that never needs to be serviced live should be marked 
with instructions to disconnect all power before servicing. If this can be done 
properly, arc flash marking may not be required. The marking may not be 
required if the equipment is installed with an external disconnect. Arc flash 
marking is generally not required for plug connected equipment.

Pick your favorite search engine and search for "arc flash labels" and you will 
find examples of the marking typically required.

Ted Eckert
Compliance Engineer
Microsoft Corporation
[email protected]

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

-----Original Message-----
From: Kunde, Brian [mailto:[email protected]]
Sent: Tuesday, November 25, 2014 6:08 AM
To: [email protected]
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Thanks for the input.

Because our products are Laboratory Equipment and not Industrial Machines, I 
assume NFPA 79 would not apply. So the SCCR on the nameplate would not be 
required. It would be difficult to provide anyway. Since we are only required 
to provide supplementary over current protection the SCCR value is really 
unknown. Our Circuit Breaker manufacturer rates their parts with a 5kA SCCR but 
to my understanding they don't even have to survive the test. So the Branch 
Circuit Breaker is relied upon to provide the protection and the necessary SCCR 
value would be based on the Customer's power system.

The SCCR value is interesting to me. For those of you who has to design your 
products to meet a specific SCCR value, what do you design for? Are there 
typical values you shoot for? How high of value must you design for? So if you 
design for say 10kA and your customer wants 50kA what do you do?

Thanks for the information regarding Arc Flash. I'm assuming that if our 
chassis (fire enclosure) meets the constructional requirements of IEC/EN/UL 
61010-1 that it should contain an Arc Flash; especially with a 230VAC powered 
instrument where the energy to produce an Arc Flash is somewhat limited. I have 
also been asked by customers if our chassis meet the NEMA requirements. I 
assume the question is in regards to Arc Flash.

Thanks again for the info. It was most helpful.

The Other Brian


-----Original Message-----
From: Mr. Doug Nix C.E.T. [mailto:[email protected]]
Sent: Monday, November 24, 2014 4:32 PM
To: [email protected]
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Dave, Brian,

Electrical field inspectors commonly require that labels of the type I 
referenced be installed by the manufacturer. The detailed labels with the arc 
flash degree and the details on the PPE requirements can only be installed post 
installation and post arc-flash hazard analysis. This is a workplace 
requirement, and not a manufacturer requirement.

Dave is correct about the Short-Circuit Withstand Rating (SCCR). This has been 
part of the nameplate requirements for many years.

Doug

On 24-Nov-14, at 16:10, Nyffenegger, Dave <[email protected]> wrote:

> Over the years recently there has been more emphasis on arc flash due to 
> injuries.  You can search on it.  The issue is the potential for arc flash 
> when the control panels are open and powered by the electrician which can 
> cause clothing to catch fire.  It's not so much an issue of containing an arc 
> flash within the enclosure, a fire enclosure should do this regardless.
>
> I asked our NRTL test engineer about arc flash warning label requirements a 
> few months ago and he pointed out that wording in NFPA 70 states that arc 
> flash warning labels are to be applied on site during machine installation.  
> There is not a requirement for the manufacturer to apply the warning.  I 
> don't have my copy of NFPA 70 in front of me but I recall I confirmed the 
> wording.   I recall I also confirmed the same on the OSHA web site.  These 
> labels can be purchased off the shelf.
>
> NFPA-79: Sec. 16.4 requires the SCCR of electrical control panels to be put 
> on the product nameplate.  UL 508A:  Supplement SB has instructions for 
> determining SCCR.  If your product doesn't contain an electrical control 
> panel and no internal branch circuits you may not need the rating.
>
> I've only had an NRTL certify to NFPA 79 for field labeling/marking.
>
> -Dave
>
> -----Original Message-----
> From: Kunde, Brian [mailto:[email protected]]
> Sent: Monday, November 24, 2014 3:29 PM
> To: [email protected]
> Subject: [PSES] Arc Flash Requirements NFPA 79
>
> Our company produces Laboratory Equipment. We design to the IEC/EN/UL 61010-1 
> series of standards and the NFPA 70 NEC.
>
> Some of our instruments can be quite large; slightly bigger than an upright 
> piano. They typically are powered by 230VAC, 20A to 50A branch circuits. It 
> is typical that our instruments are installed near or in a heavy industrial 
> environment even though they are not considered Industrial Machines. They are 
> sometimes mistaken as Industrial Machines.
>
> Recently, we have had customers ask the following questions about our 
> instruments:
>
> *       Proof that the electrical system complies to NFPA 79.
> *       Are the electrical enclosures marked for arc flash hazard per NFPA 79?
> *       What is the Short Circuit Current Rating (SCCR) of our instruments?
>
>
> Typically we simply reply that our instruments are not Industrial Machines 
> and that is that. However, if there is information we can provide that would 
> be helpful, we would like to do so.
>
> I can see where our customer may wish to power our instrument from a circuit 
> that is capable of producing very high short circuit current (SCC). If this 
> exceeds the 5kA rating of our internal Supplementary Protection Device, then 
> our customer would have to supply a Brach Circuit Breaker that can handle the 
> SCC.
>
> High SCC can also cause a concern for Arc Flash. I do not know the 
> requirements of NFPA 79 and how it affects Arc Flash. For instance,  since 
> our chassis meets the mechanical requirements called out in IEC 61010-1, is 
> it likely that our chasses will contain the arc flash hazards?
>
> Is there any part of NFPA 79 that could apply to our instruments; to the 
> mechanical or electrical system?
>
> Has something changed recently which would explain why we are now receiving 
> these type of questions?
>
> Thanks for any input or advice.
>
> The Other Brian

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to