Inrush peak for 50/60Hz transformers mostly from  magnetizing current -> core 
saturation and residual flux, and of course input V. As the saturation curve 
does not extend past the pi/2 inrush peak, any further inrush past a few mSec 
is typically from filling up the coulomb buckets on the secondary side. This is 
a tau-based thing, so both DCR and Z would be used to determine the 
current-interrupt component's expected I2T. Inrush for the 'small' transformer 
is being discussed can have peak inrush well over 20x rated continuous. For the 
smaller industrial control stuff under 5kVA, series thermistor in lieu of fuse 
is common where wire and breaker are correctly sized.

The AHJ's focus should be on SCCR, which is inversely proportional to the DCR 
of the secondary windings, and coordination between the distribution breaker 
and the fuse. Perhaps you can distract the assessment person with a Bugs Bunny 
or Daffy Duck cartoon on your pad/laptop.

Brian

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to