Hi Rich and all others,

Thanks for your explanation, make things more clear.
I still don't understand if the smaller capacitor with 2 points breaks down, 
then a current should flow (I think that's the definition or result of 
"breaking down") but if the larger capacitor with 2 planes still did not break 
down, then there can be no current flowing. Unless the explanation is like Joe 
said:
2)      In the example you used of an AC mains barrier in series with an 
Ethernet barrier, the AC mains supply typically has far more capacitance across 
its barrier than the Ethernet barrier.  Note that in the case of Ethernet, the 
Ethernet transceiver can be damaged even if the AC mains barrier does not 
suffer catastrophic breakdown.  Even the small amount of current that couples 
through the capacitance of the AC mains barrier can be sufficient to damage 
some Ethernet port designs

Do you have an idea about the question that the breakdown of 2 insulations does 
not equal the sum of both?

Best regards
Kris Carpentier,

From: Richard Nute [mailto:[email protected]]
Sent: vrijdag 12 juni 2015 21:48
To: Carpentier Kristiaan; [email protected]
Subject: RE: [PSES] Series Isolation



Hi Kris:


I'm also interested to understand the process of the breakdown of 2 isolations 
in series, like how can 1 insulation break down when the other did not yet.

Think of two capacitors in series.  Even though there is no conductor at the 
center point of the two capacitors, the voltage divides between the two 
capacitors inversely proportional to the capacitance.  That is, the smaller 
voltage is across the larger capacitor and the larger voltage is across the 
smaller capacitor.

If one of the capacitor's dielectric is air, most of the voltage will appear 
across the air capacitor, while a small amount of voltage will appear across 
the solid dielectric.  This is because the dielectric constant of air is 1, 
while the dielectric constant of a solid dielectric is more than 1 (assuming 
the area of the capacitor plates is the same).

Thus, the air dielectric capacitor has more than half of the total voltage and 
can break down while the solid dielectric capacitor has less than half of the 
total voltage and does not break down.

This same phenomenon can occur when the capacitance is determined by the area 
of the plates rather than different dielectric constants.  Consider a 
worst-case of one capacitor comprised of two points and the other capacitor 
comprised of two planes.  In this case, the smaller capacitor is the one 
comprised of two points, and will break down while the other capacitor 
comprised of two planes will not break down.

Hope this explanation helps.


Best regards,
Rich






From: Carpentier Kristiaan [mailto:[email protected]]
Sent: Friday, June 12, 2015 8:06 AM
To: [email protected]<mailto:[email protected]>
Subject: [PSES] Series Isolation

Hi group,

When 2 isolation components are put in series, my experience is that the total 
isolation breakdown voltage measured with an impulse voltage (ex. 1.2/50us) is 
always smaller than the sum of both.
An example could be the isolation between 2 transformers, for example between 
the AC mains (transformer AC-SELV) and an Ethernet transformer (SELV-ETH). 
Another example could be between 2 open relay contact, with each contact 2.5kV 
but the sum "only" 3.5kV.
Does anyone know of literature that explains this phenomenon?
I'm also interested to understand the process of the breakdown of 2 isolations 
in series, like how can 1 insulation break down when the other did not yet.

Thanks & best regards
Kris Carpentier,

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to