Ken says

"I seem to recall Michel Mardiguian writing that the relaxed dm could
transform into cm causing big problems.  That seems counter-intuitive at
best."

 

 

Think about it this way.  DM is being transmitted along a wire PAIR that we
must view as an rf transmission line, which is balanced UNTIL it meets some
discontinuity.

 

( What discontinuity? 

-       A branch cable with a single-pole switch that is open, leaving a
branch wire hanging on the other pole.

-       A device with a single class X capacitor from neutral to ground.

-       A solid ground connection to the neutral wire.

-       A wide separation between Line and Neutral conductor (Think 2-way
light switching)

-       - etc )

 

At a discontinuity that is unbalanced relative to ground (as all the above
are), there is conversion of DM power into CM because unequal amounts of the
balanced power in each wire are diverted to ground. 

The maths. are complicated because of the various and different values of
Characteristic impedance Zo between wires and from each wire to ground, but
the mechanism for power transfer is clear.

 

There have been studies of this in the last 10/15 years suggesting that
typical power transfer coupling from DM to CM in a real mains power network
at 230 volts ( I do not know of any at 115 volts, perhaps others do.)
involves only about 10dB power loss at some frequencies where the wiring is
resonant.

 

So whilst there may be a case for allowing a bit more DM than CM, there can
be no technical case for allowing 20dB or more of excess DM.  Not on
ordinary power distribution circuits.

 

 

Richard

 

Richard Marshall Laboratories,

30 Ox Lane, Harpenden, Herts.,    AL5 4HE, UK 

+44 (0)1582 460815      <http://www.design-emc.co.uk> www.design-emc.co.uk

Member of the EMC Industry Association

 

From: Ken Javor [mailto:[email protected]] 
Sent: 30 March 2016 21:59
To: [email protected]
Subject: Re: [PSES] Commom mode current vs. differential mode current and
LISN

 

With the dm limit 20 dB relaxed, the dm filter design would be simplified.
As I said, an industry study said it would save $35 million a year for the
power supply industry. I'm not sure if it was Art Wall as much as the old
guard who were involved in the original work not liking a fresh look at it.

I seem to recall Michel Mardiguian writing that the relaxed dm could
transform into cm causing big problems.  That seems counter-intuitive at
best. The opposite is way more likely. So my takeaway was that they didn't
want to consider a change to how they had set thing up.

Ken Javor
Ph. (256) 650-5261 




  _____  

From: "Grasso, Charles" <[email protected]
<mailto:[email protected]> >
Date: Wed, 30 Mar 2016 19:01:00 +0000
To: Ken Javor <[email protected]
<mailto:[email protected]> >, "[email protected]
<mailto:[email protected]> " <[email protected]
<mailto:[email protected]> >
Conversation: [PSES] Commom mode current vs. differential mode current and
LISN
Subject: RE: [PSES] Commom mode current vs. differential mode current and
LISN

Hello Ken - I remember the setup and demo to Art Wall of the FCC during the
1999 EMC Symposium here in Denver.
In spite of your best efforts it was clear that Art was not "persuaded" !!
 
The impact on the industry (as I recall) would be much cheaper filters.(if
any).
 
 

Best Regards
Charles Grasso
Compliance Engineer
Echostar Communications
(w) 303-706-5467
(c) 303-204-2974
(t) [email protected] <mailto:[email protected]> 
(e) [email protected] <mailto:[email protected]> 
(e2) [email protected] <mailto:[email protected]> 
 

From: Ken Javor [mailto:[email protected]] 
Sent: Tuesday, March 29, 2016 3:48 PM
To: [email protected] <mailto:[email protected]> 
Subject: Re: [PSES] Commom mode current vs. differential mode current and
LISN

The report on which the old 48 dBuV class B CE limit was based did develop
that based on the conducted susceptibility of AM and shortwave radios, but
it also noted that limit functioned as an adequate control for common mode
noise that would radiate as per Doug's observation. Back in the late '90s I
presented a detailed test report to TC77 showing that if instead of
controlling conducted emissions at each LISN port, they instead controlled
by modes, that dm could be relaxed 20 dB to 68 dBuV and the committee took
an action item and back then said if that were implemented, it would save
the power supply industry $35 million a year.  The work I did was based on
using the LISNMATE / LISNMARK technology as injection tools injecting pure
cm and dm and showing that the susceptibility to dm was 20 dB less, because
of bulk filter caps on the secondary of power supplies, whereas there were
no Y-caps and no cm filtering. The reason this was missed back in 1977/78
when the report was written was they used a single LISN with neutral through
the case.  CM and DM flowed in the same path.

Ken Javor
Ph. (256) 650-5261 

  _____  

From: Doug Smith <[email protected] <mailto:[email protected]> >
Reply-To: <[email protected] <mailto:[email protected]> >
Date: Tue, 29 Mar 2016 14:31:20 -0700
To: <[email protected] <mailto:[email protected]> >, Ken
Javor <[email protected] <mailto:[email protected]> >
Subject: Re: [PSES] Commom mode current vs. differential mode current and
LISN

Hi Ken and the group,

 

I always thought that the FCC measures the wrong quantity for conducted
emmissions. What shoud be measured is all conductors (two or three including
phase/neutral/protective earth) together as common mode current as that is
what radiates from the long power lines causing problems for shortwave
receivers and Amateur Radio Operators. The old demonstration of conducted
EMI into AM radios is not so useful, especially today.

 

Below 30 MHz, most devices are not large enough to radiate efficiently, but
the power wiring is long enough to radiate. I have a case of EMI in my house
from two Feit Electric LED floodlights that meet conducted emissions, but I
can't use a hand held, battery powered, shortwave receiver when the two are
on except to walk quite a distance from that part of the house. The FCC test
may catch this case, but apparently not for me, as there are only two wires
but that is not the case for other devices.

 

So phase+neutral could be noisy with respect to protective earth but as long
as it is balanced by an opposite current on protective earth, radiation
should be low.

 

Any other Amateur Radio operators want to weigh in on this?

 

Doug (K4OAP, since 1959)

 






On Tue, 29 Mar 2016 16:13:58 -0500, Ken Javor <[email protected]
<mailto:[email protected]> > wrote:


Re: [PSES] Commom mode current vs. differential mode current and LISN
Disagree. Westin had it right. A current probe can be used to isolate either
cm or dm current. If at any frequency the signal amplitude on individual
line and neutral conductors are very close, then all you can say is that at
that frequency either cm or dm predominates, but you can't say which.  With
a LISN, a separate device must be used. Mark Nave of EMC Services designed a
three port device (connects to each LISN port and to the EMI receiver)
trademarked LISNMATE in the 1980s to isolate common mode, and sometime later
he produced LISNMARK, which isolated DM.  Within the past decade, Ray Adams
while at Fischer Custom Communications packed both functions in one piece of
equipment, which if memory serves was named LISNUP.

 EMC Services, Mark Nave's company, is no longer producing his products, but
I believe the FCC product is still available.

 Ken Javor
 Ph. (256) 650-5261 


  _____  


From: Elliott Martinson <[email protected]
<mailto:[email protected]> >
Reply-To: Elliott Martinson <[email protected]
<mailto:[email protected]> >
Date: Tue, 29 Mar 2016 20:36:18 +0000
To: <[email protected] <mailto:[email protected]> >
Conversation: [PSES] Commom mode current vs. differential mode current and
LISN
Subject: Re: [PSES] Commom mode current vs. differential mode current and
LISN

http://www.hottconsultants.com/techtips/CM_vs_DM%20Conducted_Emission.html
This is a great resource for your question.
  
 Your second point kind of contradicts your first, if it's trying to say
what I think it is. DM and CM each show up on L, but the same is true for N.
It's a linear combination of both, so even if L and N are almost equal, you
can't say anything about the proportion of DM to CM currents.
  
 If they are not equal, then this implies current is travelling back via the
ground conductor and/or energy's being lost to radiated emissions.
  
 What you need is a physical circuit to do the adding/subtracting of the
LISN outputs. (otherwise your 3rd bullet point is correct)
  
 Your 4th bullet, well I refer you to the link above.
  

Elliott Martinson
Product Assurance Specialist I
Electronic Theatre Controls
3031 N PLEASANT VIEW RD
 MIDDLETON WI 53562-4809
Work: 608.824.5696 / Cell: 608.209.9897
[email protected] <mailto:[email protected]>
<[email protected] <mailto:[email protected]>
> 
  

From: Amund Westin [mailto:[email protected]]
<mailto:[email protected]%5D> <mailto:[email protected]%5D>  
Sent: Tuesday, March 29, 2016 1:23 PM
To: [email protected] <mailto:[email protected]> 
Subject: [PSES] Commom mode current vs. differential mode current and LISN

Please correct me, if I am wrong (that happens quite often .):

.        Let one wire (L) pass through a current clamp, and you measure the
combination of current mode and differential mode currents

.        Do the same with wire N. If L and N are (almost) equal, you either
have major part of DM currents or major part of CM current

.        Let both wire (L and N) pass through a current clamp, and you
measure the only CM current (DM is canceled)

.         When doing conducted emission test by LISN, you actually get what
you get. LISN do not see the difference between CM or DM. From LISN
measurements, you can't say if noise is CM or DM.

B.regards

Amund













 -
----------------------------------------------------------------
 This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

 All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

 Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

 Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)  <http://www.ieee-pses.org/list.html>
<http://www.ieee-pses.org/list.html> 
 List rules: http://www.ieee-pses.org/listrules.html 

 For help, send mail to the list administrators:
 Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

 For policy questions, send mail to:
 Jim Bacher <[email protected] <mailto:[email protected]> >
 David Heald <[email protected] <mailto:[email protected]> > 
 -
----------------------------------------------------------------

 This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

 All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

 Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

 Website:      http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to
unsubscribe)  <http://www.ieee-pses.org/list.html>
<http://www.ieee-pses.org/list.html> 
 List rules:     http://www.ieee-pses.org/listrules.html 

 For help, send mail to the list administrators:
 Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

 For policy questions, send mail to:
 Jim Bacher  <[email protected] <mailto:[email protected]> >
 David Heald <[email protected] <mailto:[email protected]> > 

 -
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
&LT;[email protected]&GT;

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
 Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)  <http://www.ieee-pses.org/list.html>
<http://www.ieee-pses.org/list.html> 
 List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
 Scott Douglas &LT;[email protected]&GT;
 Mike Cantwell &LT;[email protected]&GT;

For policy questions, send mail to:
 Jim Bacher &LT;[email protected]&GT;
David Heald &LT;[email protected]&GT;


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)  <http://www.ieee-pses.org/list.html>
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to