Bostjan;

That is my understanding; use the table to determine the cross-sectional
area (as wire) required, and then ensure that the stud&nut
arrangement provides at least triple that contact area.

-Ken

On Wed, Nov 30, 2016 at 11:33 PM, Boštjan Glavič <[email protected]>
wrote:

> Hi Ken,
>
>
>
> Thanks.
>
> So on short, if table 3B brings requirement of 50mm2 conductor, you would
> accept terminal if it brings contact area of 150mm2?
>
>
>
> Best regards,
>
> Bostjan
>
>
>
>
>
>
>
> *From:* IBM Ken [mailto:[email protected]]
> *Sent:* Thursday, December 1, 2016 5:24 AM
> *To:* Boštjan Glavič <[email protected]>
> *Cc:* [email protected]
> *Subject:* Re: [PSES] dimension of the stud for PE
>
>
>
> Hi Bostjan!
>
> Can note (c) in Table 3E be applied to this product?
>
>
>
> I think it is justifiable to extend the protective bonding rules to the PE
> connection; i.e. to pass the bonding test or to verify via inspection that
> the PE conductor is "not smaller" than the mains supply - but that's just
> my opinion.
>
>
>
> -Ken
>
>
>
> On Wed, Nov 30, 2016 at 10:53 PM, Boštjan Glavič <[email protected]>
> wrote:
>
> Dear experts
>
>
>
> I hope there are some experts dealing with IEC 60950-1 standard. We have a
> product that has rated input current 130A. Unit is intended for permanent
> connection to mains and provide special terminals for 3 phases and bolt
> with stud for PE connectio.
>
>
>
> Question is how should we evaluate dimension of this PE stud according to
> clause 2.6.4.2, 3.3.5 and table 3E of IEC 60950-1 since values in the table
> go only up to 80A rated current.
>
>
>
> Thank you for your support.
>
>
>
> Best regards,
>
> Bostjan
>
>
>
>
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to &LT;
> [email protected]&GT;
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas &LT;[email protected]&GT;
> Mike Cantwell &LT;[email protected]&GT;
>
> For policy questions, send mail to:
> Jim Bacher &LT;[email protected]&GT;
> David Heald &LT;[email protected]&GT;
>
>
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>