I can confirm Mr. Larkin’s and Mr. Woodgate’s statements.

The UK and Ireland have a national difference for IEC 60950-1 reads as follows.

2.7.1: In the United Kingdom, to protect against excessive currents and 
short-circuits in the PRIMARY CIRCUIT of DIRECT PLUG-IN EQUIPMENT, tests 
according to 5.3 shall be conducted, using an external protective device rated 
30 A or 32 A. If these tests fail, suitable protective devices shall be 
included as integral parts of the DIRECT PLUG-IN EQUIPMENT, so that the 
requirements of 5.3 are met.

Here is the corresponding national difference for IEC 62368-1.

B.3.1 and B.4: To protect against excessive currents and short-circuits in the 
primary circuit of direct plug-in equipment, tests according to Annexes B.3.1 
and B.4 shall be conducted using an external miniature circuit breaker 
complying with EN 60898-1, Type B, rated 32A.  If the equipment does not pass 
these tests, suitable protective devices shall be included as an integral part 
of the direct plug-in equipment, until the requirements of Annexes B.3.1 and 
B.4 are met.

Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: John Woodgate [mailto:[email protected]]
Sent: Monday, December 5, 2016 5:58 AM
To: [email protected]
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply

It's in 62389-1 as well.

With best wishes DESIGN IT IN! OOO – Own Opinions Only
www.jmwa.demon.co.uk<http://www.jmwa.demon.co.uk/> J M Woodgate and Associates 
Rayleigh England

Sylvae in aeternum manent.

From: Matthew Larkin [mailto:[email protected]]
Sent: Monday, December 5, 2016 1:48 PM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply

I believe there is a UK Special National Condition in EN60950-1 that states 
fault tests shall be conducted with an external 30A or 32A protection device 
and if the Direct Plug In Equipment fails the requirements of fault tests a 
protection device shall be fitted as an integral part of the Direct Plug In 
Equipment.

Best Regards

Matthew

Matthew Larkin
Samsung Electronics (UK) Ltd


From: Richard Nute [mailto:[email protected]]
Sent: 04 December 2016 19:17
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply


Do you have any recommendation of reference book about UK system requiring the 
use of fuse protection?

My recollection is the U.K. Wiring Regulations.

Best wishes for the holiday season,
Rich

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to