Ralph

Following on from John W's post, some larger properties will have more than
2 ring-mains, plus a number of dedicated branches/spurs/radials for larger
loads such as cookers, fixed water heaters and so on. In additional
branches/spurs/radials can be used for areas where the ring approach might
not be appropriate for physical reasons - such as adjacent sheds, garages
and so on - and these would be over-current limited to the cable ratings
because the diversity principle obviously cannot be applied.

Thus, normal domestic ring main circuits would be required in 2.5mm "twin
and earth" cable (another fairly unique UK concept where the grounding
conductor is reduced in size) and be protected by a 32A breaker, whereas
branch/spur/radial using the same cable must be protected by 16A breakers.

BTW: UK fuses and breakers generally follow the IEC standards approach and
are rated for continuous running at the stated rating, in contrast to the
N.American convention where the fuses/breakers are rated their blow-ratings
- thus a 16A UK/IEC breaker can be run at 16A continuous whereas a
N.American 15A breaker cannot be run continuously run at 15A.

John E Allen
W.London, UK.


-----Original Message-----
From: Ralph McDiarmid [mailto:[email protected]] 
Sent: 15 December 2016 18:30
To: [email protected]
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply

An interesting design philosophy which has benefits,  but it seems to rely
on pluggable appliances having an appropriate size fuse in their cordage.

You could for example wire an entire house with 3 or 4 of these circuits,
rather than a panel full of circuit breakers so common in N.Am

Ralph McDiarmid
Product Compliance
Engineering
Solar Business
Schneider Electric




*Please consider the environment before printing this e-mail
        


-----Original Message-----
From: John Woodgate [mailto:[email protected]]
Sent: Monday, December 12, 2016 1:50 PM
To: Ralph McDiarmid <[email protected]>;
[email protected]
Subject: RE: [PSES] British question, about a BS1363 plug-in power supply

A 32 A breaker connects to a loop of 2.5 mm^2 3-core cable (line, neutral
and protective). A large number (there is a limit but it's complicated) of
13 A wall outlets can be connected to this ring, relying on diversity to
keep the total current below 32 A.

With best wishes DESIGN IT IN! OOO - Own Opinions Only www.jmwa.demon.co.uk
J M Woodgate and Associates Rayleigh England

Sylvae in aeternum manent.


-----Original Message-----
From: Ralph McDiarmid [mailto:[email protected]]
Sent: Monday, December 12, 2016 7:34 PM
To: [email protected]
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply

What's a "ring circuit" ?


Ralph McDiarmid
Product Compliance
Engineering
Solar Business
Schneider Electric




From: Richard Nute [mailto:[email protected]]
Sent: Saturday, December 03, 2016 12:01 PM
To: [email protected]
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply


I understood the fuse in the U.K. plug was to protect the power cordage.  In
the U.K., outlets are supplied by a ring circuit rather than a branch
circuit, therefore the power cord could exceed its ampacity (a U.S.A. term).
So, if no power cord, no need for a fuse in the plug.
I wonder if the power supply has a fuse to protect the power supply.  If so,
would this count as the plug fuse?

Rich


From: John Woodgate [mailto:[email protected]]
Sent: Saturday, December 03, 2016 5:01 AM
To: mailto:[email protected]
Subject: [PSES] British question, about a BS1363 plug-in power supply

I received a 5 W SMPS plug-in power supply as part of a multi-unit product.
It has interchangeable pins for EU, US, Australian and UK  sockets, but it
has no fuse. I think this is illegal and intend to notify Trading Standards,
as the overall product is marketed by a prominent European company and is
widely offered on the Internet.
Is there any exemption at all for the requirement that a BS 1363 plug in any
form must have a fuse?

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<mailto:[email protected]> All emc-pstc postings are archived and searchable
on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <mailto:[email protected]> Mike Cantwell
<mailto:[email protected]> For policy questions, send mail to:
Jim Bacher <mailto:[email protected]>
David Heald <mailto:[email protected]>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<mailto:[email protected]> All emc-pstc postings are archived and searchable
on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <mailto:[email protected]> Mike Cantwell
<mailto:[email protected]> For policy questions, send mail to:
Jim Bacher <mailto:[email protected]>
David Heald <mailto:[email protected]>
________________________________
 This message was scanned by Exchange Online Protection Services.
________________________________

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to
unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to