That said, I would think that very few properties have just a 32A breaker at 
the in-coming supply entry point (in fact I don't think that the normal 32A 
breaker has the "prospective current" breaking capacity to be permitted for it 
to be the main entry protective device). In most there will be a  "consumer 
unit"/panel with a larger 60A or 100A main breaker, which feeds a bank of 
smaller breakers: 32A for each ring main, 20A or 40A for large spurs for fixed 
heating equipment, and (mostly) 6A for each lighting circuit (which is not are 
ring main circuits).

Then (back to the original question!) each of the pluggable appliances will 
have fused plug, and any spurs and fixed small appliances, connected to a ring 
must have a fused-spur unit (using the same fuses as in the plugs, so 13A max).

Also, in modern installations, there is required to be a Residual Current 
Device ("RCD") breaker (or GFCI in N.American parlance) for covering all the 
ringmain circuits and another one for the lighting circuits (for very good 
reasons as I know from "experience"). However, older installations may only 
have one RCD on the power circuits and very old installations (even many early 
ringmain installations) won't have them at all unless they have been 
substantially updated over the years.

Note: the above comment about RCDs is the case in urban areas, but in remote 
areas of the country, with very long supply cables to properties, you may find 
Voltage-Operated breakers instead of RCDs to ensure that the internal "house 
metalwork" doesn't  rise above acceptable limits (due to leakage currents etc.) 
w.r.t. the surrounding earth/ground conditions. Don't know much about those or 
how they are installed and so I can't give any details.

John E Allen
W.London, UK

-----Original Message-----
From: John Woodgate [mailto:[email protected]] 
Sent: 17 December 2016 08:37
To: [email protected]
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply

Before breakers were mandatory, a 30 A fuse could be used instead.

With best wishes DESIGN IT IN! OOO – Own Opinions Only www.jmwa.demon.co.uk J M 
Woodgate and Associates Rayleigh England

Sylvae in aeternum manent.


-----Original Message-----
From: Scott Xe [mailto:[email protected]]
Sent: Saturday, December 17, 2016 5:39 AM
To: John Woodgate <[email protected]>; [email protected]
Subject: Re: [PSES] British question, about a BS1363 plug-in power supply


John,

Is the 32A breaker an IRE requirement and every household must comply 
regardless how old the house is?  On one occasion, some UK engineers told me 
that a small group of house in UK and EU still do not have such 32A breaker 
installed.  Thus the equipment complying with LVD Directive may not be safe in 
abnormal operation.

Scott
    
    -----Original Message-----
    From: John Woodgate [mailto:[email protected]] 
    Sent: Monday, December 12, 2016 1:50 PM
    To: Ralph McDiarmid <[email protected]>;
    [email protected]
    Subject: RE: [PSES] British question, about a BS1363 plug-in power supply
    
    A 32 A breaker connects to a loop of 2.5 mm^2 3-core cable (line, neutral
    and protective). A large number (there is a limit but it's complicated) of
    13 A wall outlets can be connected to this ring, relying on diversity to
    keep the total current below 32 A.
    
    With best wishes DESIGN IT IN! OOO - Own Opinions Only www.jmwa.demon.co.uk
    J M Woodgate and Associates Rayleigh England
    
    Sylvae in aeternum manent.
    
    
    -----Original Message-----
    From: Ralph McDiarmid [mailto:[email protected]]
    Sent: Monday, December 12, 2016 7:34 PM
    To: [email protected]
    Subject: Re: [PSES] British question, about a BS1363 plug-in power supply
    
    What's a "ring circuit" ?
    
    
    Ralph McDiarmid
    Product Compliance
    Engineering
    Solar Business
    Schneider Electric
    
    
    
    
    From: Richard Nute [mailto:[email protected]]
    Sent: Saturday, December 03, 2016 12:01 PM
    To: [email protected]
    Subject: Re: [PSES] British question, about a BS1363 plug-in power supply
    
    
    I understood the fuse in the U.K. plug was to protect the power cordage.  In
    the U.K., outlets are supplied by a ring circuit rather than a branch
    circuit, therefore the power cord could exceed its ampacity (a U.S.A. term).
    So, if no power cord, no need for a fuse in the plug.
    I wonder if the power supply has a fuse to protect the power supply.  If so,
    would this count as the plug fuse?
    
    Rich
    
    
    From: John Woodgate [mailto:[email protected]]
    Sent: Saturday, December 03, 2016 5:01 AM
    To: mailto:[email protected]
    Subject: [PSES] British question, about a BS1363 plug-in power supply
    
    I received a 5 W SMPS plug-in power supply as part of a multi-unit product.
    It has interchangeable pins for EU, US, Australian and UK  sockets, but it
    has no fuse. I think this is illegal and intend to notify Trading Standards,
    as the overall product is marketed by a prominent European company and is
    widely offered on the Internet.
    Is there any exemption at all for the requirement that a BS 1363 plug in any
    form must have a fuse?
    
    -
    ----------------------------------------------------------------
    This message is from the IEEE Product Safety Engineering Society emc-pstc
    discussion list. To post a message to the list, send your e-mail to
    <mailto:[email protected]> All emc-pstc postings are archived and searchable
    on the web at:
    http://www.ieee-pses.org/emc-pstc.html
    Attachments are not permitted but the IEEE PSES Online Communities site at
    http://product-compliance.oc.ieee.org/ can be used for graphics (in
    well-used formats), large files, etc.
    Website: http://www.ieee-pses.org/
    Instructions: http://www.ieee-pses.org/list.html
    List rules: http://www.ieee-pses.org/listrules.html
    For help, send mail to the list administrators:
    Scott Douglas <mailto:[email protected]> Mike Cantwell
    <mailto:[email protected]> For policy questions, send mail to:
    Jim Bacher <mailto:[email protected]>
    David Heald <mailto:[email protected]>
    
    ______________________________________________________________________
    This email has been scanned by the Symantec Email Security.cloud service.
    ______________________________________________________________________
    -
    ----------------------------------------------------------------
    This message is from the IEEE Product Safety Engineering Society emc-pstc
    discussion list. To post a message to the list, send your e-mail to
    <mailto:[email protected]> All emc-pstc postings are archived and searchable
    on the web at:
    http://www.ieee-pses.org/emc-pstc.html
    Attachments are not permitted but the IEEE PSES Online Communities site at
    http://product-compliance.oc.ieee.org/ can be used for graphics (in
    well-used formats), large files, etc.
    Website: http://www.ieee-pses.org/
    Instructions: http://www.ieee-pses.org/list.html
    List rules: http://www.ieee-pses.org/listrules.html
    For help, send mail to the list administrators:
    Scott Douglas <mailto:[email protected]> Mike Cantwell
    <mailto:[email protected]> For policy questions, send mail to:
    Jim Bacher <mailto:[email protected]>
    David Heald <mailto:[email protected]>
    ________________________________
     This message was scanned by Exchange Online Protection Services.
    ________________________________
    
    -
    ----------------------------------------------------------------
    This message is from the IEEE Product Safety Engineering Society emc-pstc
    discussion list. To post a message to the list, send your e-mail to
    <[email protected]>
    
    All emc-pstc postings are archived and searchable on the web at:
    http://www.ieee-pses.org/emc-pstc.html
    
    Attachments are not permitted but the IEEE PSES Online Communities site at
    http://product-compliance.oc.ieee.org/ can be used for graphics (in
    well-used formats), large files, etc.
    
    Website:  http://www.ieee-pses.org/
    Instructions:  http://www.ieee-pses.org/list.html (including how to
    unsubscribe)
    List rules: http://www.ieee-pses.org/listrules.html
    
    For help, send mail to the list administrators:
    Scott Douglas <[email protected]>
    Mike Cantwell <[email protected]>
    
    For policy questions, send mail to:
    Jim Bacher:  <[email protected]>
    David Heald: <[email protected]>
    
    
    ______________________________________________________________________
    This email has been scanned by the Symantec Email Security.cloud service.
    ______________________________________________________________________
    
    -
    ----------------------------------------------------------------
    This message is from the IEEE Product Safety Engineering Society emc-pstc
    discussion list. To post a message to the list, send your e-mail to
    <[email protected]>
    
    All emc-pstc postings are archived and searchable on the web at:
    http://www.ieee-pses.org/emc-pstc.html
    
    Attachments are not permitted but the IEEE PSES Online Communities site at
    http://product-compliance.oc.ieee.org/ can be used for graphics (in
    well-used formats), large files, etc.
    
    Website:  http://www.ieee-pses.org/
    Instructions:  http://www.ieee-pses.org/list.html (including how to
    unsubscribe)
    List rules: http://www.ieee-pses.org/listrules.html
    
    For help, send mail to the list administrators:
    Scott Douglas <[email protected]>
    Mike Cantwell <[email protected]>
    
    For policy questions, send mail to:
    Jim Bacher:  <[email protected]>
    David Heald: <[email protected]>
    
    -
    ----------------------------------------------------------------
    This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>
    
    All emc-pstc postings are archived and searchable on the web at:
    http://www.ieee-pses.org/emc-pstc.html
    
    Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
    
    Website:  http://www.ieee-pses.org/
    Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe)
    List rules: http://www.ieee-pses.org/listrules.html
    
    For help, send mail to the list administrators:
    Scott Douglas <[email protected]>
    Mike Cantwell <[email protected]>
    
    For policy questions, send mail to:
    Jim Bacher:  <[email protected]>
    David Heald: <[email protected]>
    

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to