Hello All,

We have a base design that passed testing (exhibiting no damage) using a 
1.2u/50uS open-circuit of 15kV, and an 8/20uS current peak of 7.5kA, as per 
IEC61000-4-5. (This product did not include the extra design features that I 
proposed earlier, only basic surge suppression, and a fuse rated for higher 
energy).
I believe that the internal surge impedance is specified for this test 
equipment, but I don't know it offhand.
Testing used 5 positive and 5 negative pulses for each of Line-Ground, Line 
-Neutral, and Neutral- Ground.

My impression was that in case of a short-circuited or leaky surge suppression 
device, the primary fusing might not be of a value that would not open soon 
enough to prevent possible shock hazard from leakage.  Therefore a secondary 
series fuse, or series spark gap device would be required to stop this 
condition.

Best Regards,
Brian C.
________________________________
Brian Ceresney
Regulatory Lead
Delta-Q Technologies Corp.
3755 Willingdon Avenue, Burnaby,
B.C. Canada. V5G 3H3
Confidentiality Notice: This email message, including any attachments, is for 
the sole use of the intended recipient(s) and may contain confidential and 
privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.



From: John Woodgate [mailto:[email protected]]
Sent: August-22-17 10:06 AM
To: Brian Ceresney <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]>
Subject: RE: [PSES] Surge Suppression - Dos, and Don'ts

>From what impedance? I know that these are successive questions, but without 
>information about the source, nothing can be reliably designed. Standards in 
>the IEC 62561 series might help with information.


sage is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to