The rating on a North American circuit breaker is not its trip current. It is 
the rated current. UL 489 requires circuit breakers to hold at their rated 
current. In fact, at normal room temperatures, UL 489 Listed circuit breaker 
should hold at 110% of its rated current. The calibrations are done at 135% and 
200% of the rated current. Because the circuit breakers are packed together in 
a panel, there is heating from adjacent breakers. It is assumed that a breaker 
is typically operating at an elevated temperature. The breakers typically have 
both magnetic and thermal trip mechanisms and there is some compensation for 
the heating in the breaker panel. A UL 489 Listed breaker used in isolation 
would actually hold at 135% of its rated load for a surprisingly long time. The 
trip curve for a North American breaker may be different from that of a 
European breaker. However, I think it is misleading to say that a North 
American breaker or fuse will trip at a lower current.

Let me return to Pete Perkin's original query. North American power strips 
Listed to UL 1363 are considered temporary relocatable power taps. They are 
allowed to be listed for the full current of their plug. A power strip with a 
15 A plug can be rated 15 A and does not need to be derated to 12 A. They must 
be "relocatable" and are not allowed to be permanently affixed to structure. A 
permanently affixed power strip, such as one used in a rack in a datacenter, 
can't be listed to UL 1363. A datacenter power strip will typically be UL 
60950-1 or UL 62368-1 Listed and will be rated 12 A.

NFPA 70, the U.S. National Electrical Code, only allows the continuous load to 
be 80% of the rating of the circuit. However, "continuous" is defined as 3 
hours or more. A temporary load can be rated for the full current of the 
circuit. Thus a hairdryer with a 15 A plug is allowed to pull 15 A, 1800 W. The 
assumption is that the hairdryer will not be used for more than 3 hours 
continuously.

Because a UL 1363 Listed power strip is considered a temporary power tap, it is 
considered an extension of the branch circuit and carries the branch circuit's 
rating. A datacenter power strip is a load device and is fixed in place. That 
makes it a permanent load. It is known to be used for more than 3 hours and 
thus is rated for 80% of the branch rating. (Don't complain to me about these 
rules. I didn't make them up.) In the U.S., a UL 1363  "power strip" can only 
be provided with blind keyhole slots or spring clips. It isn't permitted to 
have holes allowing it to be screwed or bolted in place.

To cause further confusion, there are also two types of circuit breakers. UL 
489 Listed Molded Case Circuit Breakers are "branch breakers". UL 1363 Listed 
power strips with more than three outlets must have a "Supplementary 
Overcurrent Protector" which will be UL 1077 Recognized. The UL 1077 
overcurrent protector is purely a thermal device and is intended to protect 
from low overloads that a magnetic UL 489 breaker may allow.

Long ago, you could occasionally find UL 1363 Recognized power strips for rack 
mounting. They carried the full rating of the plug but could be mounted into an 
equipment rack. They were Recognized instead of Listed. One of the Conditions 
of Use was that they could only be used in racks on wheels, thereby making them 
relocatable, maintaining their status as a temporary power tap. This was a 
convoluted method of allowing rack mounted power strips, and it was used only 
as a stopgap measure until testing to UL 60950-1 became common for rack mounted 
power distribution.

Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: John Allen [mailto:[email protected]]
Sent: Friday, September 15, 2017 5:55 AM
To: [email protected]
Subject: Re: [PSES] power strip details

16A/250V is the normal running current/voltage rating of general purpose Schuko 
sockets and plugs in Europe (and sometimes elsewhere).

One of the main reasons for the differences in allowable currents from mains 
outlets (and thus from connected power strips) is the differences in the 
characteristics of the protective breakers and fuses between those used in 
Europe and those used in N.America.

General purpose European /IEC breakers/fuses are rated for continuous running 
at the marked rating, whereas on the equivalent N.American breakers/fuses the 
marked rating is the trip/blow-current rating - thus (all other things being 
"equal") the protective device for a circuit protected by one of the latter 
will trip/blow at a lower current than one protected by a European/IEC device.

This essential difference can and does (encountered it many time :() cause 
considerable issues and confusion for designers when specifying the protective 
devices for equipment  which is to be used in both N.America and Europe (and 
obviously elsewhere) - then, of course, there is the related issue that the 
relevant national certifications for such protective devices are not (with the 
exception of a very few devices certified on both continents) recognized on the 
"opposite" sides of "The Pond".

John Allen
W. London, UK

From: Don Gies [mailto:[email protected]]
Sent: 15 September 2017 13:16
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] power strip details

Pete,

Before last year's TC108 meeting in Frankfurt, I purchased a German Schucko 
European Power Strip from Amazon.  It had 3 AC receptacles and 2 USB outputs.
 Its ratings are:
"Maximum Charge: 3680W,16A/250V~    "

Don Gies
[email protected]<mailto:[email protected]>
(732) 207-7828

From: John Allen [mailto:[email protected]]
Sent: Friday, September 15, 2017 4:32 AM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] power strip details

Unlike the US/Canada (etc), there is no derating factor for UK mains wall 
outlets. A 13A wall outlet can be loaded at 13A, and a twin/duplex 13A outlet 
can be loaded at 13A per outlet because the "diversity factor" principle is 
applied, i.e. it is highly unlikely in practice that both 13A outlets will be 
actually be fully loaded at the same time!

Murphy's Law may however apply at times in that both outlets could 
simultaneously be loaded at 13A - and so it is to be hoped that the wall outlet 
in question is on a UK "ring main" circuit protected by a 32A breaker, and not 
a spur/radial/branch circuit protected by a 16A breaker!

For a power strip plugged into one of those outlets, there is a (generally, as 
John W said) a 13A fuse in the plug, and so the max cumulative continuous load 
for the sockets in the strip is also 13A - unless, of course, the mfr has 
decided to give it an overall lower current rating, fitted a lower-rated fuse 
AND marked the plug with that rating. BTW: I have also occasionally seen 7A 
fuses (the fuse standard is BS1362, but, AFAIK, that only shows a few 
"standard" ratings, and not some of those which are actually sold - such as 
those listed here 
http://cpc.farnell.com/search?st=plug%20top%20fuse<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fcpc.farnell.com%2Fsearch%3Fst%3Dplug%2520top%2520fuse&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=wPYM7w6jiCCzu%2FcAE9o6b0piDWF7bM%2BNFIXPzHd%2BwGw%3D&reserved=0>)

I believe that the standard for such UK power strips is probably BS 
5733:2010+A1:2014 "General requirements for electrical accessories. 
Specification" - but don't have a copy and so can't comment in detail on what 
it requires.

John Allen
W.London, UK



From: John Woodgate [mailto:[email protected]]
Sent: 15 September 2017 07:36
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] power strip details

UK household power strips are rated at 13 A and include a 13 A fuse. Other 
fuses, normally used in plugs, are 3 A, 5 A and 10 A. I have seen a 1 A fuse, 
but they are very rare.

With best wishes DESIGN IT IN! OOO - Own Opinions Only
www.jmwa.demon.co.uk<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.jmwa.demon.co.uk%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=eSgY3nPhG3OyYNCNTK69%2Ffwpdj3rlGCfkiHXMsjg3cs%3D&reserved=0>
 J M Woodgate and Associates Rayleigh England

UK is a sovereignty, not a Zollverein-ty

From: Pete Perkins [mailto:[email protected]]
Sent: Friday, September 15, 2017 5:55 AM
To: [email protected]<mailto:[email protected]>
Subject: [PSES] power strip details

Esteemed colleagues,

                Here in North America a domestic or commercial multi-outlet 
power strip would be cord connected thru a duplex outlet protected by a 15A (or 
sometimes 20A) circuit breaker.  The max load allowed in the circuit by the US 
NEC would be (80% of 15A) 12A for the total load (or 80% of 20A) 16A on the 20A 
breaker.   Note that the US NEC requires that any device plugged into a duplex 
outlet must not use the full load capacity of the circuit - 20% must be left 
for the other outlet's load.

                Trying to understand the loading basis for a Euro power strip.  
Is the usual protection a 10A breaker? And would the power strip be rated and 
evaluated at that load level?  What other considerations come into play here?

                How about a UK power strip.   The usual protection is the 13A 
fuse in the power plug (altho smaller values seemed to be used also).  Would 
the power strip be rated and evaluated at that load level?  What other 
considerations come into play here.

                For a Japanese power strip what is the normal breaker 
protection for the installed circuit?  What would be the max rated load for the 
power strip?  What other considerations come into play here also?

                Looking forward to your replies on this issue.

:>)     br,      Pete

Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427

503/452-1201

[email protected]<mailto:[email protected]>

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=5dBvPox7C0mCx%2FMgb233Yjkfb46zriT9rOidRvvoy3I%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=JCOF2Ybff10utEHWkev4PiDn5eOv%2FTL4xCKbQSPEy14%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=eEf4QoehQXB70sNJSGMtXavZ99vUiefFeNBBMqKobyc%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=NIBbkZFTMHUztTrweht7Ifwp%2FTTSTAaal8wqyEXNmlc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=gGkEheEXEaBcAUqKye3YFEk6cf37IRqYro4nAvMpMYw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=5dBvPox7C0mCx%2FMgb233Yjkfb46zriT9rOidRvvoy3I%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=JCOF2Ybff10utEHWkev4PiDn5eOv%2FTL4xCKbQSPEy14%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=eEf4QoehQXB70sNJSGMtXavZ99vUiefFeNBBMqKobyc%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=NIBbkZFTMHUztTrweht7Ifwp%2FTTSTAaal8wqyEXNmlc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=gGkEheEXEaBcAUqKye3YFEk6cf37IRqYro4nAvMpMYw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=5dBvPox7C0mCx%2FMgb233Yjkfb46zriT9rOidRvvoy3I%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=JCOF2Ybff10utEHWkev4PiDn5eOv%2FTL4xCKbQSPEy14%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=eEf4QoehQXB70sNJSGMtXavZ99vUiefFeNBBMqKobyc%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=NIBbkZFTMHUztTrweht7Ifwp%2FTTSTAaal8wqyEXNmlc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=gGkEheEXEaBcAUqKye3YFEk6cf37IRqYro4nAvMpMYw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=5dBvPox7C0mCx%2FMgb233Yjkfb46zriT9rOidRvvoy3I%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=JCOF2Ybff10utEHWkev4PiDn5eOv%2FTL4xCKbQSPEy14%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=eEf4QoehQXB70sNJSGMtXavZ99vUiefFeNBBMqKobyc%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=NIBbkZFTMHUztTrweht7Ifwp%2FTTSTAaal8wqyEXNmlc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=gGkEheEXEaBcAUqKye3YFEk6cf37IRqYro4nAvMpMYw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=5dBvPox7C0mCx%2FMgb233Yjkfb46zriT9rOidRvvoy3I%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=JCOF2Ybff10utEHWkev4PiDn5eOv%2FTL4xCKbQSPEy14%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=eEf4QoehQXB70sNJSGMtXavZ99vUiefFeNBBMqKobyc%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=NIBbkZFTMHUztTrweht7Ifwp%2FTTSTAaal8wqyEXNmlc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C460c37fbc456443dbbb308d4fc390b53%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636410769320565642&sdata=gGkEheEXEaBcAUqKye3YFEk6cf37IRqYro4nAvMpMYw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to