Hi Brian:

 

The answers to your questions can be found here:

 

https://www.ecmag.com/section/codes-standards/requirements-gfpe

 

A GFPE is not to protect the PE conductor.  Neither is it equivalent to a GFCI 
or ELCB.

 

The requirements of when a GPFE is to be installed are spelled out in the 
National Electrical Code.

 

“A ground fault is typically not a solid or “bolted fault” condition, so 
dynamic arcing impedance is introduced in the circuit. This reduces the fault 
current seen by a standard overcurrent device and increases the time the fault 
can exist, which allows arcing faults to manifest into destructive events. 
During an arc event, ionized gas is dispersed, creating a conductive gas or 
plasma in the atmosphere surrounding the busbars within the equipment. This 
condition often rapidly escalates from an initial phase-to-ground fault event 
to a phase-to-phase short-circuit condition. This is why the NEC requires GFPE. 
Sections 210.13, 215.10, 230.95, 240.13, 517.17 and others provide GFPE 
requirements.”

 

>From this article, a GFPE is required on 277 volts and higher, 3-phase wye, 
>4-wire, rated 1000 amps or more.  

 

Best regards,

Rich

 

 

From: Kunde, Brian [mailto:[email protected]] 
Sent: Tuesday, January 30, 2018 2:04 PM
To: [email protected]
Subject: [PSES] GFCI vs GFPE

 

I’ve recently come to understand that the 30mA Ground-Fault protectors, often 
built into a circuit breaker, is intended to protect the Protective Earth 
(Safety Ground) circuit in the case of a short circuit (opening the circuit 
before the safety ground could be damaged.  It this correct?

 

Here is my question. I’m evaluating a cut-off saw (5hp) which uses water to 
keep the blade and material cool.  The manufacturer uses a 3-phase 
supplementary circuit breaker which includes the 30mA GFPE option.  This is a 
very expensive part.  When I asked them why they use the GFPE part, they 
couldn’t give me a good answer.  

 

Would such a part be required on a 3-phase motor driven cutoff saw in either 
North America or Europe?  What standard would dictate this?  

 

If the only purpose of a GFPE is to protect the Ground Circuit, on products 
that can handle shorts without damaging the ground circuit, would a GFPE still 
be necessary?

 

Where are GFPE typically used? What industry?  

 

Please educate me.  This is a new one on me.

 

Thanks,

Brian


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to