Dan,

You mention load shedding.

I have past experience with high voltage surges on the downstream side of
disconnects or circuit protection devices when there are heavy motor loads
parallel to the equipment. Depending on the mass and speed of rotating
equipment which is coasting down to a stop, the reverse EMF is capable of
producing very high voltages until the rotating mass comes to a full stop.
The solution is usually to separate the two devices. In a similar way as
done with  coordination of overcurrent protective devices.

Best of luck, Doug



On Wed, Mar 25, 2020, 7:12 PM Dan Roman <
[email protected]> wrote:

> Hi Everyone,
>
>
>
> Thank you for the responses both on and off list, it has been helpful.
> Doug, I have seen that report but it does not seem to indicate that longer
> duration overvoltages in excess of 300V are commonplace.  I have
> anecdotally heard that power supplies, even if they have past CISPR
> immunity and IEC 61000 power fault testing, can be damaged by longer
> duration voltage surges that are supposedly common in India during load
> shedding.  Our power supplies do not suffer unusual failure rates anywhere
> in the world and have been through immunity testing without any issues, but
> I have been asked to get them ready for India with the warning that we may
> have problems.  Trying to get some hard facts before I ask for a custom SKU
> only for India.  Right now while the power quality in India may be poor,
> the products are not critical and a power interruption would not be a big
> deal, so it does not seem warranted.
>
>
>
> Regards,
>
>
>
> Dan
>
>
>
>
>
> *From:* Douglas Powell [mailto:[email protected]]
> *Sent:* Wednesday, March 25, 2020 10:59 AM
> *To:* [email protected]
> *Subject:* Re: [PSES] Power quality issues in India
>
>
>
> Dan,
>
>
>
> Possibly this article will be helpful,
> http://www.forumofregulators.gov.in/Data/Reports/Power07.pdf, check into
> issues like surge, sag, swell and spikes.
>
>
>
> It's only a couple of years old.
>
>
>
> Doug
>
>
>
> -------------------------------------------------------------------
>
> *I'm here to help you succeed! Feel free to contact me with any questions
> related to product safety, certifications, risk assessment, or EMI ... at
> no obligation. I'm always happy to help!*
>
> Douglas E Powell
>
> *Vertex Compliance Consulting*
> Laporte, Colorado USA
> [email protected]
>
> http://www.linkedin.com/in/dougp01
>
>
>
>
>
>
>
>
>
> On Tue, Mar 24, 2020 at 11:41 AM sudhakar wasnik <
> [email protected]> wrote:
>
> Dan, Yes, Indian power supply system is quite notorious for surges,
> voltage fluctuations etc. Most of Telecom or other industries beef up Power
> supply system as well as use UPS,
>
> HTH,
>
> Sudhakar wasnik
>
> Sent from my iPhone
>
>
>
> On Mar 24, 2020, at 10:17 AM, Wiseman, Joshua <
> [email protected]> wrote:
>
> 
>
> Dan, in a past life I worked for a company that makes commercial ice cream
> makers like you would see in your local Dairy Queen, McDonalds, Burger
> King, etc.  For India we had to include a UPS for some of our models
> because the power there would give us problems with the controls.  I don’t
> know the details but I do recall adding a UPS option to a newer model unit
> as recently as 3 yrs ago because of it.
>
>
>
> The UPS took care of the problem for the manufacturer when I worked there.
>
>
>
> Josh
>
>
>
>
>
> *From:* Dan Roman <[email protected]>
> *Sent:* Tuesday, March 24, 2020 12:35 PM
> *To:* [email protected]
> *Subject:* [PSES] Power quality issues in India
>
>
>
> *EXTERNAL SENDER: Verify links, attachments and sender before taking
> action*
>
>
>
> Hello List!  Hope everyone is staying healthy and safe.
>
>
>
> I would like to know if anyone has experience with power quality issues in
> India related to damaging equipment and whether you find it is necessary to
> harden power supply designs specifically for India that you would not
> normally consider for other regions like the EU.  From some reading on the
> topic there seem to be power quality issues but these are largely power
> interruptions and voltage sags that would temporarily cause the product to
> stop functioning but not result in the permanent damage of a global design.
>
>
>
> I have no recent experience with India but over a decade ago I do not
> recall having any issues with equipment in data centers, but perhaps they
> had facility power conditioning so the local building infrastructure
> prevented issues.  Is the failure rate with typical consumer products
> higher in India because of power quality issues?  Are extra precautions
> necessary?
>
>
>
> Thank you.
>
>
>
> ______________________________________________________
> Dan Roman, N.C.E.
>
> Senior Member
>
> IEEE Product Safety Engineering Society
>
> mailto:[email protected] <[email protected]>
>
>
>
>
>
>
>
>
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
> <https://nam03.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cjoshua.wiseman%40orthoclinicaldiagnostics.com%7Cfcdf3686b9ea496a8bfc08d7d0114297%7C6e63ffc0c2fc4cc4b6c4666b2ce89d92%7C0%7C0%7C637206644876722273&sdata=lhy63qT7wM%2FJyJSzz7%2F8PFJKzW%2Fukkre4gXNJl3cAtQ%3D&reserved=0>
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/
> <https://nam03.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cjoshua.wiseman%40orthoclinicaldiagnostics.com%7Cfcdf3686b9ea496a8bfc08d7d0114297%7C6e63ffc0c2fc4cc4b6c4666b2ce89d92%7C0%7C0%7C637206644876722273&sdata=ciPrXHdMnx2dYiiUcDTmBar1qBeaLXHrDcE2wq3ncEg%3D&reserved=0>
> can be used for graphics (in well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> <https://nam03.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cjoshua.wiseman%40orthoclinicaldiagnostics.com%7Cfcdf3686b9ea496a8bfc08d7d0114297%7C6e63ffc0c2fc4cc4b6c4666b2ce89d92%7C0%7C0%7C637206644876732264&sdata=Em5ND%2BzDmaz6vHHmRATefqXa1N87f7JDM%2Ff0VK30eoU%3D&reserved=0>
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe)
> <https://nam03.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cjoshua.wiseman%40orthoclinicaldiagnostics.com%7Cfcdf3686b9ea496a8bfc08d7d0114297%7C6e63ffc0c2fc4cc4b6c4666b2ce89d92%7C0%7C0%7C637206644876732264&sdata=3eH6cOaXvcyvXjpbE86FHIBq7GKxU%2FV5jFp%2BlAZd3ds%3D&reserved=0>
> List rules: http://www.ieee-pses.org/listrules.html
> <https://nam03.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cjoshua.wiseman%40orthoclinicaldiagnostics.com%7Cfcdf3686b9ea496a8bfc08d7d0114297%7C6e63ffc0c2fc4cc4b6c4666b2ce89d92%7C0%7C0%7C637206644876742257&sdata=SAm8FfrRIboPslte%2BfQLDxdM9F3rWkvZRqgxzsr5ah8%3D&reserved=0>
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]>
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]>
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to &LT;
> [email protected]&GT;
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas &LT;[email protected]&GT;
> Mike Cantwell &LT;[email protected]&GT;
>
> For policy questions, send mail to:
> Jim Bacher &LT;[email protected]&GT;
> David Heald &LT;[email protected]&GT;
>
>
>
>
> --
>
>
>
> Douglas E Powell
>
> [email protected]
> http://www.linkedin.com/in/dougp01
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to &LT;
> [email protected]&GT;
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas &LT;[email protected]&GT;
> Mike Cantwell &LT;[email protected]&GT;
>
> For policy questions, send mail to:
> Jim Bacher &LT;[email protected]&GT;
> David Heald &LT;[email protected]&GT;
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to