I'm wondering if any list members can explain the rationale behind 62368-1,  in sections 6.4.8.2.2 and 6.8.8.4.  I'm looking at the 2014 edition.

Clause 6.4.6,  Control of fire spread in a PS3 circuit, states that, "/Fire spread in PS3 circuits shall be controlled by applying all of the following supplementary safeguards/:". In that clause it includes, "/by providing a fire enclosure as specified in 6.4.8./"

Clause 6.4.8.2.2, /Requirements for a fire enclosure/, states "/For circuits where the available power does not exceed 4 000 W (see 6.4.1), a fire enclosure shall comply with the requirements of Clause S.1./"  That clause then goes on to say that V-1 is acceptable....

Clause (6.4.8.4) is addressing "Separation of a PIS from a fire enclosure and a fire barrier" and is only requiring the application of the S.2 flame test, which I believe is less demanding in that only a 60 s flame is applied rather than three steps up to 120 s for the S.1 test method.  Clause 6.4.8.4 then goes on to state that a V-0 material is excluded from the requirement.  So unless I'm mistaken, this clause 6.4.8.4 (which addresses separation) is requiring a lesser flame requirement than S.1, yet goes on to exclude V-0, but not V-1.

I don't see the rationale.  I must be missing something here. The most fundamental question in my mind here is why does 6.8.8.4 allow the S.2 test method?

Thanks,

Carl


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to