Hi John:

 

My concern is an engineering-based prediction of clearances (air insulation) as 
a function of voltage.  What is the basis for the clearance tables in the 
standards?  I have never seen anything that allows me to independently verify 
the clearance dimensions as a function of voltage.  My assumption was that the 
volts per unit distance through the insulating medium was an insulator 
constant.  Not true.  The volts per unit distance is a variable and depends on 
the distance.  So, how do I generate a table of distance for each voltage?  As 
near as I know, the tables are empirical.  

 

Your hypothesis is that the V/d curves are due to non-uniformity of the 
insulator is sort-of verified by the papers listed by Adam Dixon.  However, the 
incident you describe seems to me to be due to partial discharge.  Any V/d 
non-uniformity area of the insulating medium is a candidate for partial 
discharge.  Air, because its V/d is very much less than a solid insulator V/d, 
is likely to have sufficient voltage across the void and can lead to a partial 
breakdown of the solid insulator.  In the 1950s, I doubt that we knew much of 
the theory of partial discharge.

 

Best regards,

Rich

 

 

From: John Woodgate <[email protected]> 
Sent: Tuesday, June 25, 2024 1:26 PM
To: [email protected]; [email protected]
Subject: Re: [PSES] dielectric strength question

 

I feel that those curves support the hypothesis that the variation is due to 
non-uniformity in the material. I first suggested voids (because I recall a 
spectacular failure of a line output transformer design  in the late 1950s 
whose HV winding was encapsulated in polythene. Air in the voids ionized and 
the ions gobbled up the polythene. Attempt to eliminate the voids in viscous 
molten polythene under vacuum were partly successful, but did not survive the 
moulding process. Voids are only one possibility; simple variations in density 
may be sufficient to concentrate the electric field just where it will do the 
most damage.

Can some tests be done on a solid material that has been certified to be highly 
uniform? What happens with liquids, which should be orders of magnitude more 
uniform than the average solid?

On 2024-06-25 20:35, Richard Nute wrote:

 

Thanks to Adam for all the references.  They address very thin solid 
insulations.  But they confirm that dielectric strength is not a constant for 
very small distances, and they do not have an answer as to why.  

 

My concern is verifying clearances in safety standards.  I’ve attached curves 
of three standards clearance requirements (logarithmic scale for volts per 
millimeter).  The solid curves represent the clearances in standards and are 
close to power curves (dotted lines).  The equations are for a best-fit power 
curve.

 

The solid green curve is from an old standard and depicts actual withstand 
measurements.  

 

I suspect the electric strength curves are related to the reason for Paschen’s 
finding that gases do not break down at low voltages.  

 

My objective is to predict clearance dimensions without tables.

 

Best regards,

Rich

 

 

  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected] <mailto:[email protected]>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/[email protected]/ 
<https://www.mail-archive.com/[email protected]/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: [email protected] <mailto:[email protected]> 
Rick Linford at: [email protected] <mailto:[email protected]>  

For policy questions, send mail to:
Jim Bacher at: [email protected] <mailto:[email protected]>  

  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 

-- 
OOO - Own Opinions Only
Best wishes
John Woodgate, Rayleigh, Essex UK
Keep trying

 


 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 

Virus-free. 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 www.avg.com

 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to