Hi James,

You’re overthinking this issue. Te requirement is the rating of the largest 
motor or load. If there were to be subdivisions as you suggest, those would be 
included in the requirement. They’re not asking about the motor drive (servo, 
VFD, etc.) they’re asking about the motor. So if you have a 10 kW servo motor 
on your machine, and it’s the largest motor OR the largest load (or by 
implication either of those), then that’s what needs to be on the nameplate.

The standards writers are concerned about supply conductor sizing, so the 
supply conductors need to be sized for AT LEAST that load, and likely more. The 
information is used by the electricians who are left responsible for sizing the 
supply conductors and the mains supply OCPDs that protect the supply branch 
circuit conductors up to their connection to the machine mains supply terminals.

Doug Nix
Kitchener, Ontario, Canada
[email protected]
+1 (519) 729-5704

> On Jan 20, 2026, at 16:35, James Hulbert 
> <[email protected]> wrote:
> 
> Members,
>  
> NFPA 79, 16.4.1 lists the information to be provided on a machine nameplate.  
> Included is the “Ampere rating of the largest motor or load”.  Does this 
> refer to largest AC mains driven motor?   If a machine’s largest motor is an 
> AC servo motor driven by a Servo Drive, does the rating of Servo Drive need 
> to be indicated as the “largest load”?
>  
> Jim Hulbert
>  
> This email message may contain confidential, proprietary and/or privileged 
> information. It is intended only for the use of the intended recipient(s). If 
> you have received it in error, please immediately advise the sender by reply 
> email and then delete this message. No one other than the intended recipient 
> may disclose, copy, distribute or use the information contained in this 
> message.
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> [email protected] <mailto:[email protected]>All emc-pstc 
> postings are archived and searchable on the web at: 
> https://www.mail-archive.com/[email protected]/
> 
> Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/>
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
> List rules: 
> https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
> 
> For help, send mail to the list administrators:
> Mike Sherman at: [email protected] <mailto:[email protected]>
> Rick Linford at: [email protected] <mailto:[email protected]>
> For policy questions, send mail to:
> Jim Bacher at: [email protected] <mailto:[email protected]>
> To unsubscribe from the EMC-PSTC list, click the following link: 
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
> 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to