Thank you! Jim Hulbert
From: Douglas Nix <[email protected]> Sent: Tuesday, January 27, 2026 2:31 PM To: [email protected] Subject: Re: [PSES] Machine Nameplate Data This message is from an EXTERNAL EMAIL system. Use caution and think before opening attachments, clicking links, or responding. Hi James, You're overthinking this issue. Te requirement is the rating of the largest motor or load. If there were to be subdivisions as you suggest, those would be included in the requirement. They're not asking about the motor drive (servo, VFD, etc.) they're asking about the motor. So if you have a 10 kW servo motor on your machine, and it's the largest motor OR the largest load (or by implication either of those), then that's what needs to be on the nameplate. The standards writers are concerned about supply conductor sizing, so the supply conductors need to be sized for AT LEAST that load, and likely more. The information is used by the electricians who are left responsible for sizing the supply conductors and the mains supply OCPDs that protect the supply branch circuit conductors up to their connection to the machine mains supply terminals. Doug Nix Kitchener, Ontario, Canada [email protected]<mailto:[email protected]> +1 (519) 729-5704 On Jan 20, 2026, at 16:35, James Hulbert <[email protected]<mailto:[email protected]>> wrote: Members, NFPA 79, 16.4.1 lists the information to be provided on a machine nameplate. Included is the "Ampere rating of the largest motor or load". Does this refer to largest AC mains driven motor? If a machine's largest motor is an AC servo motor driven by a Servo Drive, does the rating of Servo Drive need to be indicated as the "largest load"? Jim Hulbert This email message may contain confidential, proprietary and/or privileged information. It is intended only for the use of the intended recipient(s). If you have received it in error, please immediately advise the sender by reply email and then delete this message. No one other than the intended recipient may disclose, copy, distribute or use the information contained in this message. ________________________________ This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to [email protected]<mailto:[email protected]> All emc-pstc postings are archived and searchable on the web at: https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9Of1lDtDoA$> Website: https://ewh.ieee.org/soc/pses/ <https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9Ofc1RSnpA$> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9OfmHYKblY$> List rules: https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9OfCM2LBkg$> For help, send mail to the list administrators: Mike Sherman at: [email protected]<mailto:[email protected]> Rick Linford at: [email protected]<mailto:[email protected]> For policy questions, send mail to: Jim Bacher at: [email protected]<mailto:[email protected]> ________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9OfGqzSRTo$> ________________________________ This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to [email protected]<mailto:[email protected]> All emc-pstc postings are archived and searchable on the web at: https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9Of1lDtDoA$> Website: https://ewh.ieee.org/soc/pses/ <https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9Ofc1RSnpA$> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9OfmHYKblY$> List rules: https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9OfCM2LBkg$> For help, send mail to the list administrators: Mike Sherman at: [email protected]<mailto:[email protected]> Rick Linford at: [email protected]<mailto:[email protected]> For policy questions, send mail to: Jim Bacher at: [email protected]<mailto:[email protected]> ________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!VYZ5iB4I1Cwow-VPH6KifPuwqjlzHcg9b6TglyxmoonCQrIqxaSNm9hh38vrrOygO0OtykWVRMD2jzGu6dLEqRHXGX30p9OfGqzSRTo$> This email message may contain confidential, proprietary and/or privileged information. It is intended only for the use of the intended recipient(s). If you have received it in error, please immediately advise the sender by reply email and then delete this message. No one other than the intended recipient may disclose, copy, distribute or use the information contained in this message. - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to [email protected] All emc-pstc postings are archived and searchable on the web at: https://www.mail-archive.com/[email protected]/ Website: https://ewh.ieee.org/soc/pses/ Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to unsubscribe) List rules: https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf For help, send mail to the list administrators: Mike Sherman at: [email protected] Rick Linford at: [email protected] For policy questions, send mail to: Jim Bacher: <[email protected]> _________________________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1