Hi all, could I have some comments on the following E-stop circuit idea. 
The core idea emerging from thinking about this is to wire dangerous 
things in series(wire OR) and use the end result of this in 
parallel(wire AND). That way the E-stop chain is cut if device1 OR 
device2 OR device 3... fails, and the resulting signal stops EMC AND 
cuts power to VFD AND cuts power to servo drives AND ...

Here is what I have come up with:

start at the HAL pin E-stop-out. It will be high whenever EMC thinks 
it's OK to go out of E-stop.

E-stop-out drives the coil of a NO(normally open) relay. This relay 
connects +12 V to the beginning of the E-stop chain only if E-stop-out 
is high.

On the +12V wire, a number of NC(normally closed) switches follow: Red 
E-stop buttons (2), Limit switches(6), NC relays on the servo amps(3).

At the end of the chain we are going to have either +12V if everything 
is OK, or 0V if we are in E-stop.

Use the +12V to power the coils of three NO relays (coils in parallel):
1. one relay connects +5V to E-stop-in telling EMC everything is OK
2. one relay grounds the Poweron/ input of a Pico Systems power switch - 
that will give power to the servo drives.
3. one relay connects 230 VAC power to a VFD which powers the spindle motor

If the E-stop chain breaks for any reason all of the relays will go to 
their NO state making E-stop-in go low, cutting power to servo drives, 
and cutting power to the VFD.

If this sounds confusing there's a picture at
http://www.anderswallin.net/temp/e-stop.png
which might help... (the E-stop chain is the blue line, the VFD relay 
would obviously be two-pole, a transistor driving relay1 is needed)


Some questions I have:
-wiring three relays in parallel at the end of the chain will result in 
three times the current needed to pull one coil of the relays. Is this 
going to be a problem ? (other than that the +12V supply must cope)
-is it a good idea to just cut the AC power to the VFD in an E-stop 
situation ? are there any other better ways to safely stop the spindle ?
-should I also hardwire the servo drive amp-enable signals so that they 
go low on E-stop?
-If I connect the common terminal of the limit switches to the 
'upstream' end of the E-stop chain, can I wire the unused NO output of 
the limit switch to another HAL pin ? This way an E-stop due to a limit 
switch could be diagnosed by EMC as coming from a specific limit (+/-) 
and axis (XYZ).


thanks for any comments,

Anders

-------------------------------------------------------------------------
Take Surveys. Earn Cash. Influence the Future of IT
Join SourceForge.net's Techsay panel and you'll get the chance to share your
opinions on IT & business topics through brief surveys - and earn cash
http://www.techsay.com/default.php?page=join.php&p=sourceforge&CID=DEVDEV
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to