On 11/06/2011 11:47 PM, Kirk Wallace wrote:
>
> I read a little more from your website. I see your chicken and egg
> problem, even with the independent loop I would think the VFD's fault
> relay would be open until the VFD powers up, but you can't power up
> until the loop is closed. Obviously, I don't have my VFD's set up for
> e-stop, but I been meaning to :)
>
>    
I can't say for any other make/model, byt the Magnetek will only trip 
the fault relay
for an ACTUAL fault.  So, it will not signal fault unless it has a motor 
run command and
you power it off.  It will not signal fault on power up or power down 
UNLESS it is
running the motor at the time.

Jon

------------------------------------------------------------------------------