> -----Original Message-----
> From: Gregg Eshelman [mailto:[email protected]] 
> Sent: Sunday, June 14, 2015 4:12 AM
<snip>
> 
> If it has a 240 option on both primary and secondary, would not using 
> the 240 taps on both make it a 1:1 so putting 120 in would 
> get 120 out?
> 
> 

Yes the voltage ration will hold. You can even swap the
secondary and primary sides but there may be differences
of a few percent because the listed voltages include a
margin for internal losses.

What you cannot safely do is exceed the current rating
of any winding even though the total power is within
specifications. This is because excess current can
saturate the magnetic core which can result in suddenly
lower impedance and bad things will happen.

In the example that you gave, this would mean that you
would only be able to safely get half as much power from
the transformer.

Steve Stallings


------------------------------------------------------------------------------