On 12/20/2015 8:37 AM, Gene Heskett wrote:
> Start with a roll of flat braid equ to a 8 or 10 gauge wire. Establish a
> bolt to the case of the controller as a master ground, and make sure
> everything that references ground in the controller box is grounded at
> this bolt.
>
> Tie this bolt to the buildings static ground using that pin of the
> controllers power cable, BUT not to the building supply neutral as thats
> usually noisy as can be.  Or to a real ground rod but that may have a
> considerable damaging joltage on it when there is lightning nearby so is
> both against the NEC and would be poor practice.
I'll start here, I see 4 places where things are grounded, the encoders 
all have a ground connection to the electrical cabinet and one on the 
other cabinet where the VFD lives. I know without looking that every 
panel has the neutral bonded to ground and I have two ground rods one 
for the house and one for the garage/shop (one panel for each one back 
to back). I do think this is local to the machine as I have other 
machines in the shop that do not have this problem. Let me study the 
grounds a bit...
> Then extend that ground, using this braid, to the bridgeports main
> casting, and perhaps also to the table and knee as the lube oil in the
> ways might preclude a really good ground on the table without it.
>
> Extend that ground from that bolt to the computers case if it is
> separated from the controller box.
>
> This is called a star ground system, where everything is common at this
> bolt.  If you can disconnect each wire from that bolt, and still measure
> continuity of 200 ohms or less from the bolt to the disconnected wire,
> then that wire has an unwanted ground somewhere, run it down and remove
> it, you want that to be "grounded" only at that bolt.
>
> The idea is that even if it does bounce a bit from a nearby lightning
> strike, it all bounces in unison with no big voltage drops between
> anything that can damage it, or induce noise that would be miss-detected
> as a signal.
>
> Years ago when I was screwing with vz & their bad copper, I figured on
> losing a modem everytime I heard thunder. Getting PO'd, I first opened
> up the wall a bit, pulled out the duplex that was going to power what I
> had in mind, and soldered all the connections in that box. Then I bought
> the biggest surge arrestor I could find, one that had phone line & cable
> tv arrestors in it.  And I bought the biggest home UPS I could find.
> Everything in this room but the lights is plugged in either to that UPS
> or that surge arrestor, and both are plugged into this all soldered
> duplex. Now lightning can hit the pole my transformer is on, possibly
> bouncing everything in this room by 100 kilovolts, but it all bounces in
> unison and I haven't lost a modem or anything else that I could
> associate the loss with local lightning strikes. But since I did get,
> from a wired keyboard I was typing on at the time, a really good jolt
> thru my fingers like shuffling ones feet on the rug and then grabbing
> the doorknob, but it didn't hurt the computer or the keyboard, but I now
> use wireless keyboard and mice.
>
> If the frame of the bridgeport is grounded thru other means, such as a
> 3rd pin on a power cable, this should be defeated in order to remove the
> potential ground loop which can be a source of quite a bit of induced
> noise.
>
> Motor drive, and feedback cables from the motors should be shielded, with
> the shields cut off at the motor ends of the cable but tied to this bolt
> at the controller end, thereby interrupting that potential ground loop.
>
> The general idea is to have one common "ground" point, even if its is not
> an earthen ground. That s/b, by the NEC, at the service entrance, a
> minimum of two full rods driven 6 feet apart, with an 8 gauge wire
> bonding them to the buildings static ground for the 3rd pin of all the
> duplexes and neutral from the pole drop, the only place it is legal to
> interconnect them.  Hanging an amprobe on any of the bare static wires
> in the service box should get you a zero reading regardless of what is
> powered up.  If you do see a reading, something out on that circuit is
> miss-wired. Fix it. Its just good practice.
>
> It and I, may sound arbitrary John, but it works.  And its NEC legal.
> If you have a decent scope, just waving a probe around with the gain
> turned up near suspected noise sources can be very educational.
>
> I've had to follow too many electricians around, fixing their mix-n-match
> attitude about static and neutral being the same thing, way too many
> times.
>
> Let us know what you did find when you've cleaned up the problem, please.
>
> Cheers, Gene Heskett


------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to