On 12/25/2015 11:51 PM, John Thornton wrote:
[snip]
> So from the distribution blocks the
> 240v goes to the VFD filter and the control transformer. I have a second 
> filter for the 120v side, should that go just after the control transformer?

Could you make a (quick and dirty) drawing?

The mains filter should normally be on the primary side, not the
secondary. A mains filter is to prevent injection back into the grid.

If I understand you correctly, you want to do following:


[240V mains]--+--[vfd filter]--[VFD controller]--[spindle]
              |
              +--[mains filter]--[ctl transformer]--[control]

The interesting part in now how earth is connected in the "VFD
controller" and the "control". If the GND of both are connected to earth
(internally), then you will create a loop and all hell may break loose.

-- 
Greetings Bertho

(disclaimers are disclaimed)

------------------------------------------------------------------------------