I just looked at the control transformer and L1 and L2 (240v side are 
fused with type CC fuses and X1 only on the 120v side is fused with a 
slo-blow fuse. So I assume they intended X2 to be the "neutral".

JT

On 1/1/2016 10:15 AM, Gene Heskett wrote:
> On Friday 01 January 2016 07:00:31 John Thornton wrote:
>
>> Hi Gene,
>>
>> The frame is most solidly grounded. I'll do the tests in a bit. Keep
>> in mind that I have a 240v to 120v step down transformer to supply the
>> 120v not a normal house circuit. Again an effort to kill the noise.
>> Which by the way I'm running 2.7 now after changing the wires on the
>> limit/home switches to twisted pair shielded wire. I've attached the
>> VFD side wiring diagram. I assume the connection is through the
>> neutral bonding screw at the panel because the step down transformer
>> is isolated from ground.
>>
>> Happy New Year to you too.
>>
>> JT
> So this then was my 2nd guess, is the capacitative interwinding coupling
> in that transformer capable of supplying a very few microamps of actual
> current, probably less than 1 or 2. With no loads plugged in, you could
> connect either of the output phases of that transformer to machine
> frame "ground" without any fireworks which would bring the other up to
> 127 to "ground".
>
> I believe in that case I would synthesize a std 127 volt circuit out of
> the control transformers secondary by connecting the lower voltage wire
> to the machines frame, along with the static ground wire in a short bit
> of romex & using the std color code where the black wire is the high
> side of the transformers secondary, feed it to a duplex or 4 plex to
> power the computer, monitor, and any other 120 volt only loads on the
> machine as long as the total load is within the ratings of the
> transformer.
>
> That should be 100% safe for everything.  And it should reduce the
> coupled noise just because its all bouncing in unison.
>
> Some of the noise coupling is coming into the 120 volt circuit from
> the "longitudinal" coupling of the windings un-avoidable capacitance,
> and grounding one side of it, and the loads static ground to the
> machines frame & ground should absorb a good share of it.
>
> In really obnoxious cases, a small, perhaps a .01 to .1 uF capacitor
> rated at least at 600 volts from the high side, black wire to the
> duplex, to the machines frame should gobble up the rest of it. And not
> just for S&G, I'd fuse the hot lead of that cap since a failure would
> take out the control transformer.  Fused at less than the transformer is
> rated of course since you want to blow the fuse instead of the
> transformer.
>
> That was my theory when I hooked this room up, and I have not lost a
> piece of gear during an electrical storm in over 10 years since I did
> it.  With the 50kw can that supplies 4 houses on the pole across the
> street, that pole has been nailed quite a few times, and I even got a
> grab the doorknob shock that jumped out of a wired keyboard once.  So I
> know this whole room full of electronics has bounced at least 25Kv. Not
> even a computer crash when it happened.
>
> Electrical shock is a weirdly defined thing. Below 20 micro-amps directly
> thru the heart, a currant so low you may not even feel it, is generally
> harmless, but at 20 micro-amps up to about 20 milli-amps it can disturb
> the beat, causing fibrillation and eventual death if no one removes the
> power or you from the source and applies the defibber paddles.
>
> Above 20 milli-amps, the survival rate is better because the heart is
> frozen, and when the currant is removed, and it hasn't been frozen so
> long you are brain dead from lack of oxygen, then the heart will often
> start back as if nothing has happened.
>
> Your trivia factoid for the day. :)
>
> My ex had a cousin that I met once in the 1970's after he had stuck an
> alu ladder he was carrying into a low hanging 7200 volt line. Lost part
> of a foot, and the shoulder blade and arm the ladder was laying on.
> Never was the sharpest tack in the box, but I'd have guessed him at an
> IQ of 105 to 110 or so after the event.  Some surgery, a specially built
> boot and a while to heal, which he was still doing when I met him at
> some sort of a family doin's, but by now he's probably taken over the
> painting business his father started 50+ years ago and run it, if not
> retired from it. That was a "few" thousand  days ago. :)  The ex left 31
> years ago, ending any excuse I had to keep track of someone in Wisconsin
> I only met once.
>
>> On 12/31/2015 5:50 PM, Gene Heskett wrote:
>>> On Thursday 31 December 2015 16:20:40 John Thornton wrote:
>>>> On the 120v side if I measure from the hot to the ground I get 79
>>>> volts, if I measure from hot to neutral I get the expected 128v...
>>>> what is that telling me?
>>>>
>>>> JT
>>> My first guess is that the Bridgeport itself, is not grounded.  It
>>> really should be, just to keep it from becoming lethally hot when
>>> somethings insulation fails.  Generally speaking, if I can measure
>>> more than a volt between neutral and the static ground, it concerns
>>> me UNLESS its a wild phase , which I don't believe you have since
>>> its not a 3 phase circuit.
>>>
>>> TBE if something is running that uses that neutral you might see
>>> more volts, but I'd re-measure after turning whatever it was off.
>>>
>>> As to the 79 volts, I would put a small light bulb (7.5 watt night
>>> lite) from the Bp frame to neutral to see if there is any real
>>> current, or its just capacitative coupling. If capacitative
>>> coupling, a 7.5 watt night light bulb will remain dark, and that
>>> voltage should drop to less than 1 or 2 volts. If it lights up at
>>> all, and the voltage doesn't drop drastically, there really is a
>>> fault someplace.  I'd start disconnecting motors for starters.
>>>
>>> Happy New Year John.
>>>
>>> Cheers, Gene Heskett
>
> Cheers, Gene Heskett


------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to