On Sun, Mar 25, 2018, at 8:29 PM, Gene Heskett wrote:
> > On Sat, Mar 24, 2018, at 5:54 PM, a k wrote:
> > > I measure supply 120 v ac.
> 
> Thats another problem, the std line voltage has been 127 volts for 
> several decades. I would at least compare what this one reads against a 
> known good meter, because either your building wiring is wonkie, or that 
> meter belongs in the trashbin, thats about a 5% error.

I beg to differ on that.  127V is NOT the standard and has never been.

The standard is 120V, with a tolerance of +/-5% at the service entrance and 
+5/-10% at the load.  
See this document: 
https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/energystatus/powerquality/voltage_tolerance.pdf
Or any number of other specs and standards.  Or simply look at the nameplate of 
any appliance or even the top of a light bulb.

If you have 127V at your house, you are actually a hair above the +5% 
tolerance.  Maybe your local power company has set the transformer taps a bit 
high to allow for voltage drop at the far end of the line, and you are stuck 
with it because you are near the transformer...

-- 