I agree with Andy. I put my controllers on a UPS and then have a signal that is wired through a drop-out relay that is also connected to the emergency stop switch. So when the power fails the machine is stopped and you can record line numbers at least and then shut down.

------ Original Message ------
From: "andy pugh" <bodge...@gmail.com>
To: "Enhanced Machine Controller (EMC)" <emc-users@lists.sourceforge.net>
Sent: 2018-11-20 17:14:59
Subject: Re: [Emc-users] UPS on controller

On Tue, 20 Nov 2018 at 15:10, Thaddeus Waldner <span> wrote:

My question is, *should* a controller such as this have an uninterruptible power supply? If so, what parts of the machine are normally served by a UPS?

I doubt that it is common to attempt to machine on standby power, but
I can see good reasons to try to keep the controller alive to perform
a controlled axis/spindle stop and graceful shutdown (including
writing to the log files, tool-table etc)

--
atp
"A motorcycle is a bicycle with a pandemonium attachment and is
designed for the especial use of mechanical geniuses, daredevils and
lunatics."
— George Fitch, Atlanta Constitution Newspaper, 1916</span>